Heat Transfer/Pressure Drop Aeration Blower Piping

Heat Transfer/Pressure Drop Aeration Blower Piping

Heat Transfer/Pressure Drop Aeration Blower Piping

(OP)
I am looking for a procedure/spreadsheet/Mathcad to calculate the exit temperature of a pipe that is used for aeration blower air.

Inlet conditions from blower are P=180 kPaA T=110C, Outlet P=100kPaA T=?.

Flow is 5965 m3/hr. Pipe is 150m DN400 2mm thick ss, ambient air temperature 40C.

The temperature is needed to determine if the outlet pipe can be metallic or thermoplastic.

I know this sounds like a homework question but it is a real situation. I only ask as I generally work with liquids and slurries.

Geoffrey D Stone FIMechE C.Eng;FIEAust CP Eng
www.waterhammer.bigblog.com.au

RE: Heat Transfer/Pressure Drop Aeration Blower Piping

Its a simple heat transfer question.  Once the pipes hit water the temperature will drop very fast, so you can usually use plastic drop pipes into water...

RE: Heat Transfer/Pressure Drop Aeration Blower Piping

                     .283
Delta T = T1( (p2/p1)      - 1)


Delta T = adiabatic temperature rise Deg K acrosss blower
T1 = absolute inlet temperature Deg K
p1 = absolute inlet pressure atm
p2 = absolute outlet pressure atm

Actual temperature rise is approximat4ed by dividing Delta T by blower efficiency.

The temperature should be around 140 to 180 Deg F.

From Wastewater Engineering, Metcalf & Eddy

RE: Heat Transfer/Pressure Drop Aeration Blower Piping

Formula did not come out correctly. It should be

 T1 X ( ((p2/p1) to 0.283 power) - 1)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources