Heat generation in waste compactors
2

Heat generation in waste compactors

Heat generation in waste compactors

(OP)
I am looking at whether the heat generated by compression within a waste compactor would be sufficient to reach the autoignition point of pentane used as a blowing agent in insulation board. The waste cut offs are compacted and whilst I suspect fires in the compactor are caused by compression heating of the pentane I need to prove this. I hated thermo at college - can anyone tell me how to go about calculating this? Is it as simple as PV=nRT?

RE: Heat generation in waste compactors

It's hard to believe, but yes you can generate enough heat to cause pentane to ignite, it's called a Diesel Cycle engine. Pentane would auto ignite in an engine at about 9 to 1 compression ratios.  There are lots of factors that may be worth exploring for a solution as a way to inhibit the auto ignition.

A large chemical plant caught on fire in Europe in the '80s as a result of commisioning a pressure gauge in the plant.  The operator purged the bordon tube gauge with nitrogen, so no air.  As he purged a small amount of the gas in the line to also assur no air was introduced.  He then opened the valve that let the gas at 800 psig into the gauge.  The nitrogen compressed and its temperature went to above 800F and the gas started to decompose and auto-burn.

RE: Heat generation in waste compactors


The temperature rise by compression can be estimated by the adiabatic equation:

Tfinal = Tinitial (P2/P1)(n-1)/n

n = Cp/Cv; for air ~ 1.4; for pentane is lower depending on P,T.

A rise in temperature may initiate spontaneous (exothermic)autooxidation eventually leading to autoignition of the impregnated insulation boards.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources