(OP)
Hi, folks,

I have a question regarding wire sizing per NEC.

UL requires hazardous voltage circuit conductors supplying one motor shall have an ampacity not less than 125% of the motor full load current rating. Does NEC have the same requirement? I found ampacity table 310-16 &17 in NEC 2005 but could not find the similar statement regarding if I need to use 125% factor.

Thanks in advance.

RE: NEC wire sizing Q

NEC requires this for ALL motors. Article 430.22

RE: NEC wire sizing Q

Just so you know also, UL is for building the equipment, NEC is for installing it. So if you already have a UL listed machine and there theoretically was a conflict over the two standards with regards to the internal wiring, the NEC would defer to the fact that the entire machine was already UL listed as an assembly.

RE: NEC wire sizing Q

(OP)
Thanks for the valuable input. More questions...

Per UL, when the control panel of equipment is designed, do we need to size the wire according to Wiring Ampacity Table AND temperature test the wire, or do just one of the two requirments?

Thanks,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources