Design letter vs. code letter on motor namplate

Design letter vs. code letter on motor namplate

Design letter vs. code letter on motor namplate

(OP)
Can anyone explain the difference between code letter and design letter date found on motor nameplates? It apperas though both are related to locked rotor current. What is the difference between the two?

RE: Design letter vs. code letter on motor namplate

NEMA Code letter (as explain in next paragraph) should not be confused with the NEMA Design letter which refers to the motor's torque curve.

NEMA CODE LETTERS FOR LOCKED-ROTOR KVA: The letter designations for locked-rotor kVA per horsepower as measured at full voltage and rated frequency.

I am usually using the NEMA Code Letters to determine LRA.

RE: Design letter vs. code letter on motor namplate

The design letter designates the shape of the torque vs. speed curve. Design B is the "standard" or most common type with 2 to 3% slip at full load. Design D is a high slip motor with high starting torque. Locked rotor current is related to the design types. You should be able to find descriptions of all of the NEMA designs in NEMA MG1, condensed version is a free download at NEMA.org.

The locked rotor code letters designate specifie ranges of locked rotor KVA per horsepower. There is a table in MG1.

RE: Design letter vs. code letter on motor namplate

You use the DESIGN letter to select the proper motor for your task based upon the torque speed curve. You then use the CODE letter in determining the electrical capacity and protection of the circuit.

JRaef.com
"Engineers like to solve problems.  If there are no problems handily available, they will create their own problems."   Scott Adams  
For the best use of Eng-Tips, please click here -> FAQ731-376

RE: Design letter vs. code letter on motor namplate

It's a 404 link now!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources