Fused Disconnect feeding breaker taps

Fused Disconnect feeding breaker taps

Fused Disconnect feeding breaker taps

(OP)
Say you have three motors individually protected off a tap by circuit breakers that was sized at 225% of NEC table 430.250 and the feeder is protected by a fused disconnect would you size the fuse at a) Largest motor breaker size + FLA of other motor taps b) same as previous, but do calculations based on the largest protection being sized at 300% of FLA? c) something else.

The code seems to support option (a) but I would think that might create an opportunity to blow the service fuse on motor start up.

RE: Fused Disconnect feeding breaker taps

(OP)
I forgot one other question: Suppose these three motors that are fed by the fused disconnect is fed by an ATS.  The largest CB motor is shut down upon power failure to lower the generator load.  Next question, do you size the generator feeder breaker based on what the service disconnect would have been sized at if that motor wasn't there or do you stick to the rule of sizing it based on the actual fuse?

RE: Fused Disconnect feeding breaker taps

I would think that you size the conductors for the feeder based upon those rules, i.e. 125% of aggregate motor FLA, then size the fuses to protect the feeder conductors. Use Time delay fuses to avoid problems with motor inrush current.

You don't size generators to fit fuses, you size generators to handle loads. Fuses are the final step and are used to protect the conductors feeding those loads.

JRaef.com
"Engineers like to solve problems.  If there are no problems handily available, they will create their own problems."   Scott Adams  
For the best use of Eng-Tips, please click here -> FAQ731-376

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources