iam working in a vacum salt plant and we need to generate hot air through multi stage heat exchanger between air from a blower and heat from direct flame using a burner
i want to decide what burner i should use so i need to know how i can calculate the heat needed to heat 154 metre cubic per minute of air from 25 degree to 150 degree at normal pressure
tanks
i want to decide what burner i should use so i need to know how i can calculate the heat needed to heat 154 metre cubic per minute of air from 25 degree to 150 degree at normal pressure
tanks





RE: hot air generator
Consider environmental pollution. Consulting with experts such as in
may be profitable at the end.
RE: hot air generator
Just an idea.
David
RE: hot air generator
First you need to convert the volume flow to a mass flow (lb/hr or Kg/hr). In metric units the density should be on the order of 1.2 kg/m^3. The actual density may be slightly more or less than this, depending on what temperature you use for the volume flow.
The specific heat of are is approx. .24 Kcal/(Kg-Deg C)
Now you can simply multiply the the three factors together to get the heat load:
Q = M X Cp X (delta T)
Regards,
Speco (www.stoneprocess.com)