Two analogs to one VFD
(OP)
I need to supply a speed reference (4-20MA) to a vfd from two separate plc systems (4-20 ma outputs) for redundancy. Would prefer to have no user input required to make the selection. Considered using a high-select analog module but this would require a separate loop supply which is problematic. Anyone have a alternative suggestion?





RE: Two analogs to one VFD
It will obviously depend on the drive you are using.
RE: Two analogs to one VFD
RE: Two analogs to one VFD
Phoenix Contact radios requires a DC power supply. The OP reveals that a loop power supply is problematic. If power is problematic for one, it's probably problematic for the other.
RE: Two analogs to one VFD
A few of the mid-range VSDs have a small set of logic elements which allow rudimentary ladder logic or a simple PID loop to be configured. Some offer expansion modules which give increased PLC-style processing with a bigger instruction set. One we've used successfully is the Control techniques Unidrive with the PLC module. There are almost certainly others with similar capability although I don't know the specific models.
----------------------------------
Sometimes I only open my mouth to swap feet...
RE: Two analogs to one VFD
I assumed that loop supply is not only power but the wire run itself. Radios commenly run on 9v-30v dc. The OPS is not running a remote loop powered device,its a VFD. I can't think of any senareo where there is a PLC and a VFD where 24v cant be made. I just had a salesmen pushing accutech equipment. These things run on battery and transmit things like temp and pressure along with analog. Havent tried anything yet but I'm thinking about it.
RE: Two analogs to one VFD
I cannot imagine that PDL was the only company to make drives with this feature, particularly as some of the newer drives I've seen are far more fancy.
RE: Two analogs to one VFD
Like the ACS-550.
RE: Two analogs to one VFD
JRaef.com
"Engineers like to solve problems. If there are no problems handily available, they will create their own problems." Scott Adams
For the best use of Eng-Tips, please click here -> FAQ731-376
RE: Two analogs to one VFD
RE: Two analogs to one VFD
while idle: any sensor indicating speed is bad
While spinning: the acceleration must be less than
a physical limit.
While both are identical: both work
so the logic can decide which sensor to believe.
----------------------------