CONTACTORS FOR AC MOTOR CENTER TEST

CONTACTORS FOR AC MOTOR CENTER TEST

CONTACTORS FOR AC MOTOR CENTER TEST

(OP)
Dear All,

We want to design an AC Motor Center Test For a small electric motor repair shop.To perform No load test.
Today They have a 3 Phase,  112.5 KVA  13.2 KV/ 220V distribution transformer Exclusive  for feed the test center, and one 3 Phase Low Voltage 112.5 KVA transformer with this features :   Primary Volts 220 and a multi tap secundary Winding : 80-150-230-380-460 Volts, any of  this winding taps can handle the 112,5 KVA. 60 Hz.

The Main Idea is Use a PLC to control the contactors and the Test center will operate applying first the 80 Volts and then secuencially the other Voltages Up to 230 or 380 or 460 Volts. The test center only will test  one motor at time , no test simultanelly.

How calculate the Contactors?? What protective device did you use?? Any other Design Ideas??

Thanks for the Inputs.

Petronila

RE: CONTACTORS FOR AC MOTOR CENTER TEST

Contactors and thermal overloads are rated based on current. Choose them according to the current they will switch. Or have I misunderstood the question?
 

----------------------------------
  Sometimes I only open my mouth to swap feet...

RE: CONTACTORS FOR AC MOTOR CENTER TEST

petronila

How about using a 0-220 V stepless, variac feeding into a 220 / 460 V testing trafo ? This way you get any voltage from 0 - 460 V without any switching / tap changing contactors ?

Of course, if the shop has 400 V supply, then can just use a 0-460 V stepless, variac ?

*Why make the same mistake twice when there so many new ones available*

RE: CONTACTORS FOR AC MOTOR CENTER TEST

The contactors should be sized for the largest motors that will be tested.
respectfully

RE: CONTACTORS FOR AC MOTOR CENTER TEST

If you want just one common contactor that switches whatever you connect to it at whatever voltage you are testing with, size the contactor for the largest motor AND the current at the lowest voltage that it will see.

As far as protection devices, if you want just one prootective device do work on anything, use something solid state that can be easilly reprogrammed for the expected current.

JRaef.com
"Engineers like to solve problems.  If there are no problems handily available, they will create their own problems."   Scott Adams  
For the best use of Eng-Tips, please click here -> FAQ731-376

RE: CONTACTORS FOR AC MOTOR CENTER TEST

Petronila, in our workshop we simply uses contactor which has the highest possible ampere machine rating that could put into test usually for general purpose motors. Other test set up, we uses simple primary liquid resitor.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources