How to figure 3 phase voltage drop
When figuring 3 phase voltage drop do you use the distance to the load or 2 times that?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
RE: How to figure 3 phase voltage drop
In single-phase circuits, with the neutral conductor size equal to the phase conductor, you'd double the distance to account for the total voltage drop (phase plus neutral).
For example, if you have 0.2 ohms resistance in each phase condutor of a 208/120V, 3-phase system and 15A of load. The VD per line will be 15A*0.2 ohm=3V, The percentage voltage drop will be 3V/120V=.025 or 2.5%. Line to line VD will be 5.2V, still 2.5% of 208V.
Same is true, it were a delta system, even if there is no physical neutral. The calcs are still done on per phase basis, using phase voltage=line voltage/1.732.
(For purists: Above example ignores reactance for simplicity.)
Once you read the correct value from the table, you multiply by twice the distance in 1 phase and simply by the distance in 3 phase.
You should be aware enough to know that as you have more applianced branched in parallel on the same circuit, you need to calculate the voltage drop chunk by chunk; other easier methods exist of course but should be a nice exercise.
Also, the impedance values are given in some catalogs for cos phi = 0.8 as well as for cos phi = 1, which is the worst case (highest resistance).
http://www.aberdare.co.za/
http://www.eurocabos.pt/ (reseller)
http://www.cabelte.pt/
http://www.generalcablecelcat.com/index.html
You can also find prices on these websites.