Transformer blows primary fuses with no load.

Transformer blows primary fuses with no load.

Transformer blows primary fuses with no load.

(OP)
We have a 5000 kva transformer wired 480 volt on the primary and 230 volt on the secondary.  This is a single phase transformer.  When you power it up three to four times it blows the both primary fuses.  What do you think is the problem.

Thanks,
RogerMM

RE: Transformer blows primary fuses with no load.

Inrush current. No doubt.

Can you change primary taps so you get less V/turns? That usually means changing to a lower secondary voltage and improves the situation a lot.

Did you say 5000 kVA? Single phase?

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Transformer blows primary fuses with no load.

What size and type of fuses are installed?  My hunch is that the fuse size is very close to the inrush of the transformer and maybe starting to melt (ie weaken) the fuse and then it finally blows.

RE: Transformer blows primary fuses with no load.

Could the core be magnetised?  I seem to remember that vacuum contactors gave this problem at one time, since they could "chop" the current, rather than interupting at current zero.  This could magnetise the core permanently, gicing rise to high inrush currents, sometimes making it difficult to reclose breakers.  This system is fused, but it could have been caused by an upstream problem.  Have there been any power supply outages?

RE: Transformer blows primary fuses with no load.

5000 kVA 480 V to 230 V single-phase???  This I would like to see.  Maybe no one makes large enough fuses looking around

Transformer inrush seems the likely culprit, I agree with the others.

Inrush current can vary significantly depending on instantaneous value of the voltage (voltage phase angle) when the transformer is energized.  So often, this type of fuse blowing occurs maybe one time out of 5 or one time out of 10.  

If you can confirm the transformer size, maybe we can make some suggestions on the fuse size.  

RE: Transformer blows primary fuses with no load.

(OP)
Your right!  The transformer is 5000 VA or 5 KVA.

RE: Transformer blows primary fuses with no load.

So how big is the fuse that is blowing?  

RE: Transformer blows primary fuses with no load.

(OP)
The fuses we are using is rated slow blow 20 amp.  We have taken all the load off the secondary.  Powering the transformer two to five times blows the fuses.

RE: Transformer blows primary fuses with no load.

Thanks - I thought so.

Are you trying to protect anything thermally with the fuses? Don't. Use fuses only as a short circuit protection. And use slow blow fuses.

If you are using fuses like 16 or 20 A, then they shall blow occasionally. Use something like 35 A.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Transformer blows primary fuses with no load.

(OP)
The fuses are Amp Trap ATDR20, 600V, AC

THANKS,
ROGERMM

RE: Transformer blows primary fuses with no load.

Also cycling the transformer in quick succession, not allowing fuse to cool off will add to the woes.

RE: Transformer blows primary fuses with no load.

Hey! We are cross-posting. Use 35 A. Or are your wires too small for that?

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Transformer blows primary fuses with no load.

Also for what it is worth, the load on transformer generally do not have the bearing on the inrush current.

RE: Transformer blows primary fuses with no load.

Actually, a loaded transformer has less inrush. The reason? Simply because there is some voltage drop in the primary so that the core doesn't get saturated as much as with no load. It may be only a few percent's worth of difference. But that may make the difference between saturated or not.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Transformer blows primary fuses with no load.

(OP)
The wire size on the primary is #8 and the secondary is #10.

RE: Transformer blows primary fuses with no load.

Sorry, I don't do AWG - only sqmm. Anyone else?

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Transformer blows primary fuses with no load.

#8 is good for 40A max.

#10 is good for 30A max.

RE: Transformer blows primary fuses with no load.

gunnar:

Thanks for your thoughts on loaded transformer.

RE: Transformer blows primary fuses with no load.

As skogsgurra has mentioned, try a larger fuse.  But you'll have to comply with NEC requirements for transformer protection, if you are in the US.  

RE: Transformer blows primary fuses with no load.

NEC says primary fuses can be 2.5X rated current when using secondary fuses and you can round up. So, you could use a 30A fuse if you're in the USA.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources