Thermal Expansion Problems Heat vrs Cold
Do you address piping configurations different for
hot applications versus cold.
Let's say you have one end of the spectrum where the
temperature is +500 Deg. F and on the other you have
-500 Deg. F. What do you do differently to prevent
moments from taking place?
Wayne E. Lovison
service-parts@naglepumps.com
RE: Thermal Expansion Problems Heat vrs Cold
No, as far as I know, cold and hot are addressed in the same manner. The temperature difference is all that matters, as long as you stay above the Code-specified minimum metal design temperature which for example, for A106B is -20° F (I think). The temperature difference is used to calculate the thermal reactions on the pump flanges.
Thermal loads may be the least of your worries. Don't forget about deadload, seismic, and pressure thrust...
Thanks!
Pete
P. J. (Pete) Chandler, PE
Principal Engineer
Mechanical, Piping, Thermal, Hydraulics
Processes Unlimited International, Inc.
Bakersfield, California USA
pjchandl@prou.com
got carried away and picked a number
forgive me for my error.
Thanks for your help
Wayne E. Lovison
Thanks!
Pete
Principal Engineer
pjchandl@prou.com