(OP)
I have this question on GFCI receptacles.  GFCI rating per UL 943, Class A stated that it should be 5 mA.  NEC Section 210.8 stated that GFCI's operate on currents of 5 mA, with +/- 1 mA differntials allowed.  Currently I am located overseas in Japan, and all the local products for GFCI's are rated at 15 mA.  In Europe (Germany) also, 15mA are common place.  My question is that whether 5mA is truly a necessity or merely a standard requirement.  My question has to do with whether 5 mA is truly a safety issue that makes 15mA a clear violation.  But then, if 15mA is truly unsafe, why would they be allowe to use in Gemrnay and Japan.  Does anyone have any experience or know the history behind this argument?

RE: GFCI receptacles

There are physiological reasons behind the 30 mA limit in RCDs. Currents below 30 mA are not lethal, if interrupted within 100 milliseconds. So, European GFCIs have a "must operate" range 15 - 30 mA at a delay no more than 100 ms. I shall try and find the reasoning behind this - I know it exists somewhere.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: GFCI receptacles

Skogs;  It probably has to do with the electrical rhythm of the heart. The heart self triggers itself for each beat. It starts at one spot of the heart and then propagates over the entire surface then goes into a rest then it starts again.  I suspect that 100ms is only a short part of a cycle and is much less likely to result in a chaotic rhythm associated with fibrillation and ultimately death.

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: GFCI receptacles

British requirements for an RCD providing personnel protection are trip at a value not exceeding 30mA  and with a tripping time not exceeding 40ms at 5x nominal tripping current. The newer standards are BS EN 61008-1 and BS EN 61009-1.
 

----------------------------------
  Sometimes I only open my mouth to swap feet...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources