Open Web Steel Joist - Depth reduction

Open Web Steel Joist - Depth reduction

Open Web Steel Joist - Depth reduction

(OP)
I have existing 24 inch deep steel joist spanning 40 feet. At one end, for about twelve feet I need to reduce the depth to 12 inches. Any ideas.

RE: Open Web Steel Joist - Depth reduction

The optimum depth for your joists should be about 28 to 30"... ' your 24" is a little shallow... and might be prone to some vibration.  Cutting it to 12" for 1/3 the span will likely cause problems... you might try something else...

Dik

RE: Open Web Steel Joist - Depth reduction

Intermediate support of the joist via column, wall, beam - at the point where the joist must be reduced.  Re-analyze the joists's shear moment diagram capacity and verify that intermediate web strengthening is OK or needs strengthening.

RE: Open Web Steel Joist - Depth reduction

(OP)
Suppose at cut we drop a column. For 12 feet we can add a steel beam and remove the joist. For the remaining joist still in service with new support at column, do we need to do any modifications or simply add vertical member (web stiffener) at column top should be fine

RE: Open Web Steel Joist - Depth reduction

I am in agreement with JAE's recommendation.

The shortened joist's web members need to be looked at in that some of those web members may have stress reversals from the original design.

RE: Open Web Steel Joist - Depth reduction

Yep - Crown06 - just to repeat - when you design a joist, it has a theoretical shear capacity that varies across the span from the original max. end reaction - to 0 at midspan.  However, the SJI requires the joist manufacturers to at least design the joist web members for 25% of the shear at the end (some years ago it was 50% so the older the joist the more hefty the webs).

When you shorten a joist span, you have the potential to create a larger shear at the new end from what it was originally designed for.  Simply construct an "original" shear diagram and superimpose it over your new shear diagram to check if you are ok.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources