frequency during power system disturbance
will we have the same frequency in all connected network during power system disturbances ?
RE: frequency during power system disturbance
Yes. There may be some phase differences, depending on how strong/weak the grid is and what currents are flowing. But frequency remains the same throughout the whole grid.
Gunnar Englund
www.gke.org
I did see an exception once, but it is very rare. This was a large island with it's own network and distributed hydro generation and co-generation. It was also fed with a DC undersea cable.
One of the largest open pit mines in the world commenced operation on the island.
The utility engineers required the mine to install underfrequency meters to trip the main incoming 140KV breaker at the mine, in the event that the DC feed was lost and the mine load started pulling the frequency down on the hydro fed system.
As I said, this is a unique situation and Gunnars answer is correct in all normal situations and systems.
Respectfully
Let my explain more, what I mean is during transients in the system due to faults, swings, etc.. , do we the same frequency variations at all buses in the interconnected network that is if we have a frequency of a certain value at one point in the network then the same value is exactly measured at any other point in the network  at the same time
Yes.
Gunnar Englund
www.gke.org
There is some problem with the whole aspect of 'the' question.
Frequency is, by definition, "something over time".  There is no "instant everywhere frequency".
Yes the frequency you measure everywhere on your network will be found to be the same over time.
The actual phase may be different, and in fact probably is different all over your network.
Keith Cress
Yes.
respectfully
Yes.
Gunnar Englund
www.gke.org
At the risk of contradicting the esteemed members above, it is possible to have different frequencies during certain system events.  The difference in frequencies will be seen more as differences in phase angle, but the difference will be there.
It requires an out-of-step (pole slipping) type of event or a severe power swing to cause this frequency difference.  If the system hangs together, the frequency differences will be relatively minor and could be treated as a rapidly changing relative phase angle.  During pole slipping there are two (or more) portions of the grip operating at different frequencies.  This should last for a very short time as the protective system will segment the system to stop the pole slipping and once that happens there are two (or more) separate systems each with its own frequency.
A seemingly simple question has evolved into a philosophical discussion relating to phase difference and whether a frequency should be considered measured over a complete period or defined as the derivative of instantaneous value. Since the latter method is both impractical and of little practical interest - I still say that frequency is the same throughout the system.
I recall a discussion we had with one of the major power companies over here. There were two paper mills. Bot owned by same guy. He had two identical 36 MW direct (electrodes dipping into water) heated electrical steam vessels and he bought cheap electricity from this energy company. Cheap, because the energy company was allowed to cut his steam generators if frequency dropped below 49.85 Hz (50 Hz grid) and thus be able to manage difficult situations.
One of the vessels was stopped a lot more often than the other, which caused two paper machines to stop. When the owner asked power company why? They answered that "since the A mill was closer to the power station than the B mill was, it was only natural that the frequency dropped faster at the B mill"
I had been asked to participate at the meeting and I asked the power company guy to say again. He did. I asked if the meeting had understood what he said. It had. Then the paper mill owner sued the power company for contract breach.
Gunnar Englund
www.gke.org
I'm going to side with David on this one - under severe system disturbances the instantaneous frequency at differing locations on the grid can vary as power flows redistribute following a major event such as loss on a large interconnector or generating site. The instantaneous frequency at a node will rise as generators move in relative phase as the load angle changes with load. System-wide frequency will also move slightly as load (or infeed) increases or decreases. The events in Europe last year (or was it 2005?) almost certainly showed this immediately prior to the European grid separating.
  Sometimes I only open my mouth to swap feet...
It surely showed different frequencies after the separation. But before? Frequency? Measured? I do not believe it changed - not if we are talking frequency as we know it from frequency counters. No.
Gunnar Englund
www.gke.org
Frequency as measured by zero crossing or other whole cycle phenomena; probably not.  Frequency as calculated from the instantaneous speed of the rotors of synchronous machines; absolutely.  If the swing is stable it is probably sufficiently accurate to assume a constant frequency and varying phase angles, but once poles start to slip there are two, or more, frequencies on the system until the system becomes two or more independent systems.
Food for thought: What is instantaneous frequency? The definition of 1Hz is the frequency of a periodic event having a duration of 1 second. Doesn't that imply a sampling interval of 1 second?! ie until you've measured a series of events for a second you don't know the true frequency. The load angles and the instantaneous speed of the individual rotors may oscillate above or below sychronous speed, but the system frequency is the same across the whole system.
Marmite
The average frequency over two or three cycles may be constant, or the same at all busses in the system.  But frequency has to change for one or more cycles in order for a phase angle change to occur.
Imagine two voltage waveforms at the same frequency and zero phase angle difference.  Now shift one voltage waveform to 30 degrees lagging. Its next zero crossing will be 30/360 = 1/12 of a cycle later.  If a voltage waveform instantaneously shifts from 0 to 30 degrees lag there has to be one half cycle where time between zero crossings is longer than normal. Frequency = 1/(time between zero crossing).  Frequency is slower during that one cycle.  Otherwise, how does the voltage go from 0 lag to 30 lag?
One-cycle measurements of frequency are not as good as averaging over several cycles.  The change in frequency caused  by a sudden phase shift would be barely discernable over three-four cycles.
For that one cycle, a slower frequency would be recorded.
Yes. I think that most of us understand that.
But the question was about frequency. And I think that the OP shall tell us what he really meant by frequency.
I repeat what I said a few hours ago: "A seemingly simple question has evolved into a philosophical discussion relating to phase difference and whether a frequency should be considered measured over a complete period or defined as the derivative of instantaneous value."
Gunnar Englund
www.gke.org
This is getting very intellectual!  How I explain generating power systems to mechanical engineers (lowest of low..) is think of a rack and pinion railway.  For non rail enthusiasts, it is like a gear laid out flat, the engine goes along by driving a gear along the rack.
See http://en.wikipedia.org/wiki/Rack_railway
Now think of it in reverse.  If the rack moves and the engines are still then that is how a power system works.  The rack drives the gears at a constant speed (frequency).  Generators push the rack, loads slow it.  In practice consider  the rack and gears to be made of rubber to allow for disturbances (faults, load changes), but the frequency is constant (speed of rack).  Even though though one may be speeding up and the other slowing.
It depends on power flow, I live in UK. If there is a sudden power demand in England, frequency will drop, Scotland will restore balance by the fact that its frequency is high, resulting in power flow to England.  System will be stable when power flow is zero, at a lower frequency.  Difference in frequency is marginal, but that’s how it works.
Other use of analogy, to synchronise you have to march the speed of the gear and the rack and get the teeth in line.
Hear! Hear! Getting your teeth in line! That is what counts!
Sorry. Had a big one to get over loss of Konrad, our cat.
Gunnar Englund
www.gke.org
I have been thionking today about phase shifts as they relate to frequency changes.
I think we all agree that an action that initiates or terminates a phase shift will cause at least one-half cycle to be distorted. I think that it is spitting hairs to call this half cycle anomaly a different frequency.
Consider a power system with a branch circuit energizing a resistance heating load. Now start a motor with a bad power factor on the same circuit. We have a phase shift, right? Different frequency for a very short time? What about the voltage? It didn't shift, only the current shifted. But we have been hearing that a phase shift causes a different frequency.
Okay, now I have two different frequencies on the same circuit. The voltage frequency no longer equals the current frequency (for a short time).
I may change my mind at some point in the future, but for now, I am not quite ready to accept different voltage and current frequencies in the same circuit, rather than calling a phase shift a phase shift.
Let's call a phase shift a phase shift and accept that it causes a distortion in the wave form, but let's not split this poor hair any further.
Pole slipping is a little more interesting. I have never slipped a really big pole, but I imagine that a fourier analysis on the system would show both the system frequency and the frequency of the problem machine. I would expect the relative percentages of the two frequencies to vary at different locations throughout the system.
respectfully
I agree - you can have short-term multiple frequencies during system disturbances.  If not, how would underfrequency loadshedding be effective at a local level?  Any underfrequency event would shed all protected load across the entire grid at the same time?
Dear you!
I am getting very tired of this.
If you are going to drag all sorts of frequency components into this discussion, then you have different frequencies all the time. I am, if you didn't get it, referring to harmonics.
You have to decide, Are you discussing frequency as measured with a frequency meter? Or are you discussing transients? Or frequency defined as d(alpha)/dt? Or are you trying to define some sort of Unidentified Frequency Object aka UFO?
We need to hear what the OP actually meant with his question. It may even be that he wasn't aware of the differences?
As to "local load shedding": There is no such thing. If grid frequency goes down, then all objects set to switch off at that frequency do switch off. No matter where in the grid they happen to be situated. There may exist load dependent extra conditions to help decide which object to shed. But then you have something else then frequency that decides.
Gunnar Englund
www.gke.org
Freaquency is stable for all the nework (in avarage) but this is not true during transients in the system, so you can find different frequencies in one system at one time (during transient, so if you are near the faul location the frequency at this piont will be effected more than the other points in the network locating so far from the piot of the fault.
I must warn against bringing current frequency into the discussion. While current has frequency, it is the voltage frequency that is usually the measured quantity or used for load shedding
Also, the harmonic frequencies are unchanging. While voltages or currents at harmonic frequencies might have changing magnitudes over the system, the harmonic frequencies themselves do not. The second harmonic on a 60 Hz fundamental system is 120 Hz where ever you are.
I was trying some irony. I hope that you agree that 180 Hz is different from 60 Hz? Then, you have different frequencies all the time.
I know - never use irony without being very clear about it. But then, what use is it?
Gunnar Englund
www.gke.org
If anyone is still interested in this thread, there is a document on Baslers website which explains the frequency swings at remote busbars during faults.
http://www.basler.com/downloads/loadshed.pdf
Marmite
Thanks for the link, Marmite.
Before we can get on the same page, we will have to agree on how to measure frequency. Do we measure peak to peak, full cycle zero crossings or half cycle zero crossings.
For example, we are familiar with the wave form of an asymetrical fault current with a DC offset. If we measure the peak to peak time of a complete cycle we will see our fundamental frequency. If we measure the zero crossing time of a complete cycle we will see a small drift in frequency as the phase shift introduced by the fault slowly decays. It can be seen that each succesive full cycle zero crossing is not at the same point on the wave form as the DC component decays.
Measuring the full cycle zero crossings will show a frequency different from the fundamental frequency but the frequency difference will follow the decay of the DC component. When the DC component has decayed to zero the zero crossing frequency difference will be zero and we will be back at fundamental frequency.
Determining the  frequency by the half cycle zero crossings will give alternating high and low frequencies for every half cycle.
I still stick to my original thought that the frequency is basically the same everywhere on the system.
Different measurment techniques may show apparently different frequencies.
Even though a DC offset or a phase shift on a wave form may look like a frequency change to a relay using zero crossing techniques, the full cycle peak to peak may well still be the fundamental frequency.
I will accept the case of the "Hunting" generator as a differend frequency, because the speed of the generator is varying, but as the excursions are limited to about plus and minus 90 degrees, I am comtent to also call this a series of phase shifts.
Note that the Basler information is at some points discussing frequency drop when a section of the grid has become islanded on overloaded, and the frequency of the islanded portion is decaying, and at some points the information is discussing "apparent' frequency shifts as determined by a relay using zero crossing determination of frequency.
What's the point?
How do we measure frequency? Half cycle, full cycle, peak to peak, zero crossing, or average.
Can we accept the small timing variation when a phase shift is introduced or must we consider this a short duration frequency change.
When I want to pick up some more load on a paralleled generator, I open the governor. The shaft assumes a new relative position a few degrees ahead of its previous position. Technically, yes, to affect the relative position change, the frequency has to have increased a very small amount for a very small time.
I'd rather call a phase shift a phase shift, and not a very limited frequency increase for a very short time.
"I also tend to call a spade a spade, rather than speaking about the dog's hysterectomy."
This is an attempt at a little humor and I hope it is taken that way. I respect all the points of view that have been presented here. I agree with most of them.
Bottom line, how do we determine frequency.
Respectfully
frequency: The number of
periods occurring per unit time.
periodic function: A function that satisfies f (x) = f (x + nk) for
all x and for all integers n, k being a constant.
First of all you need a periodic waveform.