Non bearing interior wall detail > 12'

Non bearing interior wall detail > 12'

Non bearing interior wall detail > 12'

(OP)
Using 2003 IBC will a 13' tall interior non-bearing wall using the following material pass code?

1. Studs braced with 5/8 gyp board ea. side.
2. 25 ga 3 5/8 tract and stud.
3. Bracing @ 4'-0" O.C. staggered 3 5/8 25ga.

The 2 walls are for a restroom addition and are attached to an existing demising wall and exterior wall. Wall lengths are 7'2" and 6'4".  Ceiling is 25ga 16" O.C. @ 8' with 5/8 gyp board.
Thanks in advance!!!!!

RE: Non bearing interior wall detail > 12'

Go online and look up "The Steel Network" or "MarinoWare".  They should have limiting wall height tables available.  The tables I have say no.  You need to either use a shorter wall or a heavier gage stud...say 22ga.

RE: Non bearing interior wall detail > 12'

(OP)
I checked on MarinoWare under Limiting Heights Tables (Composite) using a 3 5/8" member 358DWS25 5 PSF, L/120, and 24" O.C. it shows 13'9".  I am missing something or will this pass?  The city engineer said she was going to send over a new detail for walls over 12' and she sent the same detail that I have stating for H < 12' AND BRACING < 8'.  

RE: Non bearing interior wall detail > 12'

I wasn't using the composite wall table.  We don't use that table for our designs.  We also don't use L/120 for deflection.  We use L/240.  IBC 2003 says L/120 is acceptable for non-brittle finish.  According to that table, the wall will work.  Be sure to use a deflection track at the top of the wall if you are attaching to the bottom of beams or a floor system.

RE: Non bearing interior wall detail > 12'

(OP)
I just received an updated for the CLV NV building department stating that 20ga @ 24" o.c. is good up to 16'.  I guess I will just change the drawings and give my customer a change order.

RE: Non bearing interior wall detail > 12'

Why is an electrical person designating walls?

RE: Non bearing interior wall detail > 12'

(OP)
I was wondering if someone was going to ask me that.  I used my cad artist to draw the plans for this small TI.  We are a general contractor also, but mainly due commercial electrical.  Scope of work was only to close an opening in an existing demising wall, add restroom, 200A panel, and re-circuit elec. to new panel.  Job was too small to bring in an architect and I was told the ceiling was originally 11'.  Long story short, found out ceiling was 11'10", and the typical framing details that I am familiar with wouldn't pass.  Since I had to specify what type of professional I am, I figured I would tell the truth, instead of posing as a Structural Engineer just to ask a ?  Hope this isn't a problem.

RE: Non bearing interior wall detail > 12'

I think we can all appreciate honesty, especially since the question itself woud have given you away as non-structural.  

There is a problem though if you are practicing out of your area of expertise, partiularly if you sign and seal this work.  I hope that's not the case.  It's hard to say with an interior non-load-bearing wall, but is it worth it in the end?  I think it's worth having a professional check what you are doing.  In the end it protects you, the client and your company.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources