Adaptive remeshing problem
I am using adaptive meshing to overcome the large element distortition I have.
However, the job does not want even to start and file process is aborted due to error with the warning
mesaage;
10 elements are distorted. Either the interior angles are out of the
suggested limits or the triangular or tetrahedral quality measure is
bad. The elements have been identified in element set WarnElemDistorted.
In the Mesh Verify all the elements look fine , so i do not know what
is the problem with my use to the adaptive meshing
RE: Adaptive remeshing problem
I think the job does not start because of an error , other than the warning you posted.
There is a difference between "error" and "warning" :
- an warning message indicates that the user should be concerned more with the validity of the solution but does not preclude the ABAQUS solver obtaining a solution (more or less accurate)
- an error message usualy leads to interruption of the computational task (i.e. job).
That what i get concerning the ERROR message
"Analysis Input File Processor exited with an error".
I do not know what and where is the error
xerf
here is the input file, if you get some moments to look at it . I could not figure out what and where is the error
*Heading
** Job name: trial9 Model name: Model-3
*Preprint, echo=NO, model=NO, history=NO, contact=NO
** PARTS
*Part, name=Part-1
*End Part
** ASSEMBLY
*Assembly, name=Assembly
*Instance, name=Part-1-1, part=Part-1
*Node
      1,   80.0026169,          20.
      2,          80.,          29.
      3,           0.,          27.
      4,           0.,          20.
      5,         222.,          22.
      6,         218.,          20.
      7,         230.,          20.
      8,         226.,          22.
      9,           0.,           0.
     10,         260.,           0.
     11,         170.,          20.
     12,         260.,          20.
     13,         194.,          32.
     14,         188.,          29.
     15,         206.,          32.
     16,   80.0013123,   24.4861832
     17,   75.6777649,   28.8919449
     18,   71.3428116,   28.7835712
     19,   66.9160919,   28.6729031
     20,   62.4708633,   28.5617714
     21,   58.0138435,    28.450346
     22,    53.569603,   28.3392391
     23,   49.1115112,    28.227787
     24,   44.6444664,   28.1161118
     25,   40.1790161,   28.0044746
     26,   35.7080879,   27.8927021
     27,   31.2336788,   27.7808418
     28,   26.7571659,   27.6689301
     29,   22.2777138,    27.556942
     30,   17.8007545,   27.4450188
     31,   13.3265018,   27.3331623
     32,   8.86127567,   27.2215328
     33,   4.41305828,   27.1103268
     34,           0.,   23.5201893
     35,   4.52738857,          20.
     36,   9.05640888,          20.
     37,   13.5926247,          20.
     38,   18.1333847,          20.
     39,   22.6746693,          20.
     40,   27.2164421,          20.
     41,   31.7572861,          20.
     42,   36.2973251,          20.
     43,   40.7794151,          20.
     44,   45.2487106,          20.
     45,   49.7649574,          20.
     46,   54.2877617,          20.
     47,    58.806488,          20.
     48,   63.3272209,          20.
     49,   67.8458023,          20.
     50,   72.4132385,          20.
     51,   76.6274567,          20.
     52,         224.,          20.
     53,         228.,          21.
     54,           0.,    13.333333
     55,           0.,   6.66666651
     56,   4.90566015,           0.
     57,    9.8113203,           0.
     58,   14.7169809,           0.
     59,   19.6226406,           0.
     60,   24.5283012,           0.
     61,   29.4339619,           0.
     62,   34.3396225,           0.
     63,   39.2452812,           0.
     64,   44.1509438,           0.
     65,   49.0566025,           0.
     66,    53.962265,           0.
     67,   58.8679237,           0.
     68,   63.7735863,           0.
     69,    68.679245,           0.
     70,   73.5849075,           0.
     71,   78.4905624,           0.
     72,    83.396225,           0.
     73,   88.3018875,           0.
     74,     93.20755,           0.
     75,    98.113205,           0.
     76,   103.018867,           0.
     77,    107.92453,           0.
     78,   112.830185,           0.
     79,   117.735847,           0.
     80,    122.64151,           0.
     81,   127.547173,           0.
     82,   132.452835,           0.
     83,    137.35849,           0.
     84,   142.264145,           0.
     85,   147.169815,           0.
     86,    152.07547,           0.
     87,   156.981125,           0.
     88,   161.886795,           0.
     89,    166.79245,           0.
     90,    171.69812,           0.
     91,   176.603775,           0.
     92,    181.50943,           0.
     93,     186.4151,           0.
     94,   191.320755,           0.
     95,    196.22641,           0.
     96,    201.13208,           0.
     97,   206.037735,           0.
     98,    210.94339,           0.
     99,    215.84906,           0.
    100,   220.754715,           0.
    101,    225.66037,           0.
    102,    230.56604,           0.
    103,   235.471695,           0.
    104,   240.377365,           0.
    105,    245.28302,           0.
    106,   250.188675,           0.
    107,   255.094345,           0.
    108,         260.,   6.66666651
    109,         260.,    13.333333
    110,   165.000153,          20.
    111,    160.00029,          20.
    112,   155.000443,          20.
    113,    150.00058,          20.
    114,   145.000732,          20.
    115,    140.00087,          20.
    116,   135.001022,          20.
    117,    130.00116,          20.
    118,   125.001305,          20.
    119,   120.001457,          20.
    120,   115.001602,          20.
    121,   110.001747,          20.
    122,   105.001892,          20.
    123,   100.002037,          20.
    124,    95.002182,          20.
    125,    90.002327,          20.
    126,   85.0024719,          20.
    127,   214.411774,          20.
    128,   210.510437,          20.
    129,   206.652435,          20.
    130,   202.833649,          20.
    131,   198.631119,          20.
    132,   193.658676,          20.
    133,   188.612762,          20.
    134,   183.324066,          20.
    135,   177.560852,          20.
    136,         254.,          20.
    137,         248.,          20.
    138,         242.,          20.
    139,         236.,          20.
    140,   184.049454,   27.0247307
    141,    181.02948,   25.5147438
    142,   178.280731,   24.1403637
    143,   174.949097,   22.4745522
    144,   221.749588,   24.1252041
    145,   218.920944,   25.5395298
    146,    216.87175,    26.564127
    147,   214.822021,   27.5889874
    148,   212.409943,   28.7950268
    149,   209.527786,   30.2361107
    150,   202.005859,          32.
    151,   198.008301,          32.
    152,   183.304352,          29.
    153,   178.608688,          29.
    154,    173.91304,          29.
    155,   169.217392,          29.
    156,   164.521744,          29.
    157,    159.82608,          29.
    158,   155.130432,          29.
    159,   150.434784,          29.
    160,   145.739136,          29.
    161,   141.043472,          29.
    162,   136.347824,          29.
    163,   131.652176,          29.
    164,    126.95652,          29.
    165,   122.260872,          29.
    166,   117.565216,          29.
    167,   112.869568,          29.
    168,   108.173912,          29.
    169,   103.478264,          29.
    170,    98.782608,          29.
    171,   94.0869598,          29.
    172,    89.391304,          29.
    173,   84.6956558,          29.
    174,    75.988266,   24.4416885
    175,   71.7193375,   24.3896561
    176,   67.2882233,   24.3351536
    177,   62.8219681,   24.2798729
    178,    58.356945,   24.2244606
    179,   53.8827553,   24.1689529
    180,   49.3987198,   24.1132965
    181,   44.9151382,   24.0575333
    182,   40.4393311,   24.0017509
    183,   35.9597244,   23.9459267
    184,   31.4633102,   23.8900719
    185,   26.9611015,   23.8341942
    186,   22.4573383,    23.778286
    187,   17.9542274,   23.7224674
    188,   13.4541054,   23.6669121
    189,   8.95960236,   23.6122532
    190,    4.4750123,   23.5606918
    191,   224.666672,          21.
    192,   4.59827995,    13.333333
    193,   4.75197029,   6.66666651
    194,   9.19655991,    13.333333
    195,   9.50394058,   6.66666651
    196,   13.7948399,    13.333333
    197,   14.2559109,   6.66666651
    198,   18.3931198,    13.333333
    199,   19.0078812,   6.66666651
    200,   22.9913998,    13.333333
    201,   23.7598515,   6.66666651
    202,   27.5896797,    13.333333
    203,   28.5118217,   6.66666651
    204,   32.1879616,    13.333333
    205,   33.2637901,   6.66666651
    206,   36.7862396,    13.333333
    207,   38.0157623,   6.66666651
    208,   41.3845215,    13.333333
    209,   42.7677307,   6.66666651
    210,   45.9827995,    13.333333
    211,   47.5197029,   6.66666651
    212,   50.5810814,    13.333333
    213,   52.2716713,   6.66666651
    214,   55.1793594,    13.333333
    215,   57.0236435,   6.66666651
    216,   59.7776413,    13.333333
    217,   61.7756119,   6.66666651
    218,   64.3759232,    13.333333
    219,   66.5275803,   6.66666651
    220,   68.9741974,    13.333333
    221,   71.2795563,   6.66666651
    222,   73.5724792,    13.333333
    223,   76.0315247,   6.66666651
    224,   78.1707611,    13.333333
    225,    80.783493,   6.66666651
    226,    82.769043,    13.333333
    227,   85.5354614,   6.66666651
    228,   87.7374954,    13.333333
    229,   90.4725189,   6.66666651
    230,   92.7059555,    13.333333
    231,    95.409584,   6.66666651
    232,    97.674408,    13.333333
    233,   100.346642,   6.66666651
    234,   102.642868,    13.333333
    235,   105.283699,   6.66666651
    236,    107.61132,    13.333333
    237,   110.220757,   6.66666651
    238,   112.579781,    13.333333
    239,   115.157814,   6.66666651
    240,   117.548233,    13.333333
    241,   120.094872,   6.66666651
    242,   122.516693,    13.333333
    243,   125.031929,   6.66666651
    244,   127.485146,    13.333333
    245,   129.968994,   6.66666651
    246,   132.453598,    13.333333
    247,   134.906052,   6.66666651
    248,   137.422058,    13.333333
    249,   139.843109,   6.66666651
    250,   142.390518,    13.333333
    251,   144.780167,   6.66666651
    252,   147.358978,    13.333333
    253,   149.717224,   6.66666651
    254,   152.327438,    13.333333
    255,   154.654282,   6.66666651
    256,   157.295883,    13.333333
    257,   159.591339,   6.66666651
    258,   162.264343,    13.333333
    259,   164.528397,   6.66666651
    260,   167.232803,    13.333333
    261,   169.465454,   6.66666651
    262,   172.201263,    13.333333
    263,   174.402512,   6.66666651
    264,   177.676483,    13.333333
    265,   179.592957,   6.66666651
    266,   183.151703,    13.333333
    267,   184.783401,   6.66666651
    268,   188.626923,    13.333333
    269,   189.973831,   6.66666651
    270,   194.102142,    13.333333
    271,   195.164276,   6.66666651
    272,   199.577362,    13.333333
    273,   200.354721,   6.66666651
    274,   203.772583,    13.333333
    275,   204.905151,   6.66666651
    276,   207.967804,    13.333333
    277,   209.455597,   6.66666651
    278,   212.163025,    13.333333
    279,   214.006042,   6.66666651
    280,   216.358246,    13.333333
    281,   218.556473,   6.66666651
    282,   220.553452,    13.333333
    283,   223.106918,   6.66666651
    284,   226.188675,    13.333333
    285,   228.377365,   6.66666651
    286,   231.823898,    13.333333
    287,   233.647797,   6.66666651
    288,   237.459122,    13.333333
    289,   238.918243,   6.66666651
    290,   243.094345,    13.333333
    291,   244.188675,   6.66666651
    292,   248.729553,    13.333333
    293,   249.459122,   6.66666651
    294,   254.364777,    13.333333
    295,   254.729553,   6.66666651
    296,   198.163147,   22.7885704
    297,   197.988342,   25.6377335
    298,   197.948029,    28.667305
    299,   181.952179,   24.9286175
    300,   193.668518,   28.2451515
    301,   188.920197,   26.9193211
    302,   184.919586,   25.7411156
    303,   181.077209,   23.8134518
    304,    179.39859,   22.1069717
    305,   184.080124,   22.1456451
    306,   188.867157,   22.3808517
    307,   193.660202,   22.6626244
    308,   184.792358,   24.1007538
    309,   189.085999,   24.6954479
    310,   193.710342,   25.3575611
    311,   216.577148,   25.8388462
    312,    201.90274,   28.7153873
    313,   205.670395,   28.4849167
    314,   209.129623,   27.6854496
    315,   212.170258,   26.8654823
    316,   214.721161,   26.2214451
    317,   219.465164,   23.3846359
    318,   217.569611,   24.8388691
    319,   201.970184,   25.6725807
    320,   202.262466,   22.7982445
    321,   205.734665,   25.5083447
    322,   206.101624,   22.7236862
    323,   209.270172,   25.1371422
    324,   209.789246,   22.5862732
    325,   212.507599,   24.7698402
    326,   213.308121,   22.4908276
    327,   215.330566,   24.6093388
    328,   216.525955,   22.6212006
    329,   182.323074,   27.7722015
    330,   84.8373489,    24.503952
    331,   89.6787567,   24.5060921
    332,   94.5217743,   24.5076904
    333,   99.3652573,   24.5091305
    334,   104.208885,   24.5105247
    335,   109.052551,   24.5119038
    336,   113.896225,    24.513279
    337,   118.739914,   24.5146523
    338,   123.583595,   24.5160255
    339,   128.427277,   24.5173988
    340,    133.27095,    24.518774
    341,   138.114624,   24.5201473
    342,   142.958313,   24.5215225
    343,   147.802002,   24.5228958
    344,   152.645676,   24.5242691
    345,   157.483887,   24.5326748
    346,   162.294769,   24.5762367
    347,   167.004059,   24.7606392
    348,   171.296829,    25.463932
    349,   175.418686,   26.2951336
    350,   179.287613,   27.1168346
*Element, type=CPE4P
 1,   1,  16, 174,  51
 2,  16,   2,  17, 174
 3,  51, 174, 175,  50
 4, 174,  17,  18, 175
 5,  50, 175, 176,  49
 6, 175,  18,  19, 176
 7,  49, 176, 177,  48
 8, 176,  19,  20, 177
 9,  48, 177, 178,  47
10, 177,  20,  21, 178
11,  47, 178, 179,  46
12, 178,  21,  22, 179
13,  46, 179, 180,  45
14, 179,  22,  23, 180
15,  45, 180, 181,  44
16, 180,  23,  24, 181
17,  44, 181, 182,  43
18, 181,  24,  25, 182
19,  43, 182, 183,  42
20, 182,  25,  26, 183
21,  42, 183, 184,  41
22, 183,  26,  27, 184
23,  41, 184, 185,  40
24, 184,  27,  28, 185
25,  40, 185, 186,  39
26, 185,  28,  29, 186
27,  39, 186, 187,  38
28, 186,  29,  30, 187
29,  38, 187, 188,  37
30, 187,  30,  31, 188
31,  37, 188, 189,  36
32, 188,  31,  32, 189
33,  36, 189, 190,  35
34, 189,  32,  33, 190
35,  35, 190,  34,   4
36, 190,  33,   3,  34
37,   5,   6,  52, 191
38,  52,   7,  53, 191
39,  53,   8,   5, 191
 40,   4,  54, 192,  35
 41,  54,  55, 193, 192
 42,  55,   9,  56, 193
 43,  35, 192, 194,  36
 44, 192, 193, 195, 194
 45, 193,  56,  57, 195
 46,  36, 194, 196,  37
 47, 194, 195, 197, 196
 48, 195,  57,  58, 197
 49,  37, 196, 198,  38
 50, 196, 197, 199, 198
 51, 197,  58,  59, 199
 52,  38, 198, 200,  39
 53, 198, 199, 201, 200
 54, 199,  59,  60, 201
 55,  39, 200, 202,  40
 56, 200, 201, 203, 202
 57, 201,  60,  61, 203
 58,  40, 202, 204,  41
 59, 202, 203, 205, 204
 60, 203,  61,  62, 205
 61,  41, 204, 206,  42
 62, 204, 205, 207, 206
 63, 205,  62,  63, 207
 64,  42, 206, 208,  43
 65, 206, 207, 209, 208
 66, 207,  63,  64, 209
 67,  43, 208, 210,  44
 68, 208, 209, 211, 210
 69, 209,  64,  65, 211
 70,  44, 210, 212,  45
 71, 210, 211, 213, 212
 72, 211,  65,  66, 213
 73,  45, 212, 214,  46
 74, 212, 213, 215, 214
 75, 213,  66,  67, 215
 76,  46, 214, 216,  47
 77, 214, 215, 217, 216
 78, 215,  67,  68, 217
 79,  47, 216, 218,  48
 80, 216, 217, 219, 218
 81, 217,  68,  69, 219
 82,  48, 218, 220,  49
 83, 218, 219, 221, 220
 84, 219,  69,  70, 221
 85,  49, 220, 222,  50
 86, 220, 221, 223, 222
 87, 221,  70,  71, 223
 88,  50, 222, 224,  51
 89, 222, 223, 225, 224
 90, 223,  71,  72, 225
 91,  51, 224, 226,   1
 92, 224, 225, 227, 226
 93, 225,  72,  73, 227
 94,   1, 226, 228, 126
 95, 226, 227, 229, 228
 96, 227,  73,  74, 229
 97, 126, 228, 230, 125
 98, 228, 229, 231, 230
 99, 229,  74,  75, 231
100, 125, 230, 232, 124
101, 230, 231, 233, 232
102, 231,  75,  76, 233
103, 124, 232, 234, 123
104, 232, 233, 235, 234
105, 233,  76,  77, 235
106, 123, 234, 236, 122
107, 234, 235, 237, 236
108, 235,  77,  78, 237
109, 122, 236, 238, 121
110, 236, 237, 239, 238
111, 237,  78,  79, 239
112, 121, 238, 240, 120
113, 238, 239, 241, 240
114, 239,  79,  80, 241
115, 120, 240, 242, 119
116, 240, 241, 243, 242
117, 241,  80,  81, 243
118, 119, 242, 244, 118
119, 242, 243, 245, 244
120, 243,  81,  82, 245
121, 118, 244, 246, 117
122, 244, 245, 247, 246
123, 245,  82,  83, 247
124, 117, 246, 248, 116
125, 246, 247, 249, 248
126, 247,  83,  84, 249
127, 116, 248, 250, 115
128, 248, 249, 251, 250
129, 249,  84,  85, 251
130, 115, 250, 252, 114
131, 250, 251, 253, 252
132, 251,  85,  86, 253
133, 114, 252, 254, 113
134, 252, 253, 255, 254
135, 253,  86,  87, 255
136, 113, 254, 256, 112
137, 254, 255, 257, 256
138, 255,  87,  88, 257
139, 112, 256, 258, 111
140, 256, 257, 259, 258
141, 257,  88,  89, 259
142, 111, 258, 260, 110
143, 258, 259, 261, 260
144, 259,  89,  90, 261
145, 110, 260, 262,  11
146, 260, 261, 263, 262
147, 261,  90,  91, 263
148,  11, 262, 264, 135
149, 262, 263, 265, 264
150, 263,  91,  92, 265
151, 135, 264, 266, 134
152, 264, 265, 267, 266
153, 265,  92,  93, 267
154, 134, 266, 268, 133
155, 266, 267, 269, 268
156, 267,  93,  94, 269
157, 133, 268, 270, 132
158, 268, 269, 271, 270
159, 269,  94,  95, 271
160, 132, 270, 272, 131
161, 270, 271, 273, 272
162, 271,  95,  96, 273
163, 131, 272, 274, 130
164, 272, 273, 275, 274
165, 273,  96,  97, 275
166, 130, 274, 276, 129
167, 274, 275, 277, 276
168, 275,  97,  98, 277
169, 129, 276, 278, 128
170, 276, 277, 279, 278
171, 277,  98,  99, 279
172, 128, 278, 280, 127
173, 278, 279, 281, 280
174, 279,  99, 100, 281
175, 127, 280, 282,   6
176, 280, 281, 283, 282
177, 281, 100, 101, 283
178,   6, 282, 284,  52
179, 282, 283, 285, 284
180, 283, 101, 102, 285
181,  52, 284, 286,   7
182, 284, 285, 287, 286
183, 285, 102, 103, 287
184,   7, 286, 288, 139
185, 286, 287, 289, 288
186, 287, 103, 104, 289
187, 139, 288, 290, 138
188, 288, 289, 291, 290
189, 289, 104, 105, 291
190, 138, 290, 292, 137
191, 290, 291, 293, 292
192, 291, 105, 106, 293
193, 137, 292, 294, 136
194, 292, 293, 295, 294
195, 293, 106, 107, 295
196, 136, 294, 109,  12
197, 294, 295, 108, 109
198, 295, 107,  10, 108
199, 135, 134, 305, 304
200, 134, 133, 306, 305
201, 133, 132, 307, 306
202, 132, 131, 296, 307
203, 304, 305, 308, 303
204, 305, 306, 309, 308
205, 306, 307, 310, 309
206, 307, 296, 297, 310
207, 303, 308, 302, 299
208, 308, 309, 301, 302
209, 309, 310, 300, 301
210, 310, 297, 298, 300
211, 298, 151,  13, 300
212, 300,  13,  14, 301
213, 301,  14, 140, 302
214, 302, 140, 141, 299
215, 141, 142, 303, 299
216, 142, 143, 304, 303
217, 143,  11, 135, 304
218, 151, 298, 312, 150
219, 150, 312, 313,  15
220,  15, 313, 314, 149
221, 149, 314, 315, 148
222, 148, 315, 316, 147
223, 147, 316, 311, 146
224, 298, 297, 319, 312
225, 297, 296, 320, 319
226, 296, 131, 130, 320
227, 312, 319, 321, 313
228, 319, 320, 322, 321
229, 320, 130, 129, 322
230, 313, 321, 323, 314
231, 321, 322, 324, 323
232, 322, 129, 128, 324
233, 314, 323, 325, 315
234, 323, 324, 326, 325
235, 324, 128, 127, 326
236, 315, 325, 327, 316
237, 325, 326, 328, 327
238, 326, 127,   6, 328
239, 316, 327, 318, 311
240, 327, 328, 317, 318
241, 328,   6,   5, 317
242,   5,   8, 144, 317
243, 317, 144, 145, 318
244, 318, 145, 146, 311
245, 152, 153, 350, 329
246, 153, 154, 349, 350
247, 154, 155, 348, 349
248, 155, 156, 347, 348
249, 156, 157, 346, 347
250, 157, 158, 345, 346
251, 158, 159, 344, 345
252, 159, 160, 343, 344
253, 160, 161, 342, 343
254, 161, 162, 341, 342
255, 162, 163, 340, 341
256, 163, 164, 339, 340
257, 164, 165, 338, 339
258, 165, 166, 337, 338
259, 166, 167, 336, 337
260, 167, 168, 335, 336
261, 168, 169, 334, 335
262, 169, 170, 333, 334
263, 170, 171, 332, 333
264, 171, 172, 331, 332
265, 172, 173, 330, 331
266, 173,   2,  16, 330
267,  16,   1, 126, 330
268, 330, 126, 125, 331
269, 331, 125, 124, 332
270, 332, 124, 123, 333
271, 333, 123, 122, 334
272, 334, 122, 121, 335
273, 335, 121, 120, 336
274, 336, 120, 119, 337
275, 337, 119, 118, 338
276, 338, 118, 117, 339
277, 339, 117, 116, 340
278, 340, 116, 115, 341
279, 341, 115, 114, 342
280, 342, 114, 113, 343
281, 343, 113, 112, 344
282, 344, 112, 111, 345
283, 345, 111, 110, 346
284, 346, 110,  11, 347
285, 347,  11, 143, 348
286, 348, 143, 142, 349
287, 349, 142, 141, 350
288, 350, 141, 140, 329
289, 140,  14, 152, 329
*Nset, nset=_PickedSet4, internal
   1,   4,   6,   7,   9,  10,  11,  12,  35,  36,  37,  38,  39,  40,  41,  42
  43,  44,  45,  46,  47,  48,  49,  50,  51,  52,  54,  55,  56,  57,  58,  59
  60,  61,  62,  63,  64,  65,  66,  67,  68,  69,  70,  71,  72,  73,  74,  75
  76,  77,  78,  79,  80,  81,  82,  83,  84,  85,  86,  87,  88,  89,  90,  91
  92,  93,  94,  95,  96,  97,  98,  99, 100, 101, 102, 103, 104, 105, 106, 107
 108, 109, 110, 111, 112, 113, 114, 115, 116, 117, 118, 119, 120, 121, 122, 123
 124, 125, 126, 127, 128, 129, 130, 131, 132, 133, 134, 135, 136, 137, 138, 139
 192, 193, 194, 195, 196, 197, 198, 199, 200, 201, 202, 203, 204, 205, 206, 207
 208, 209, 210, 211, 212, 213, 214, 215, 216, 217, 218, 219, 220, 221, 222, 223
 224, 225, 226, 227, 228, 229, 230, 231, 232, 233, 234, 235, 236, 237, 238, 239
 240, 241, 242, 243, 244, 245, 246, 247, 248, 249, 250, 251, 252, 253, 254, 255
 256, 257, 258, 259, 260, 261, 262, 263, 264, 265, 266, 267, 268, 269, 270, 271
 272, 273, 274, 275, 276, 277, 278, 279, 280, 281, 282, 283, 284, 285, 286, 287
 288, 289, 290, 291, 292, 293, 294, 295
*Elset, elset=_PickedSet4, internal, generate
  40,  198,    1
*Nset, nset=_PickedSet9, internal
   5,   6,   7,   8,  52,  53, 191
*Elset, elset=_PickedSet9, internal, generate
 37,  39,   1
*Nset, nset=_PickedSet11, internal
   5,   6,   8,  11,  13,  14,  15, 127, 128, 129, 130, 131, 132, 133, 134, 135
 140, 141, 142, 143, 144, 145, 146, 147, 148, 149, 150, 151, 296, 297, 298, 299
 300, 301, 302, 303, 304, 305, 306, 307, 308, 309, 310, 311, 312, 313, 314, 315
 316, 317, 318, 319, 320, 321, 322, 323, 324, 325, 326, 327, 328
*Elset, elset=_PickedSet11, internal, generate
 199,  244,    1
*Nset, nset=_PickedSet12, internal
   1,   2,  11,  14,  16, 110, 111, 112, 113, 114, 115, 116, 117, 118, 119, 120
 121, 122, 123, 124, 125, 126, 140, 141, 142, 143, 152, 153, 154, 155, 156, 157
 158, 159, 160, 161, 162, 163, 164, 165, 166, 167, 168, 169, 170, 171, 172, 173
 329, 330, 331, 332, 333, 334, 335, 336, 337, 338, 339, 340, 341, 342, 343, 344
 345, 346, 347, 348, 349, 350
*Elset, elset=_PickedSet12, internal, generate
 245,  289,    1
*Nset, nset=_PickedSet13, internal
   1,   2,   3,   4,  16,  17,  18,  19,  20,  21,  22,  23,  24,  25,  26,  27
  28,  29,  30,  31,  32,  33,  34,  35,  36,  37,  38,  39,  40,  41,  42,  43
  44,  45,  46,  47,  48,  49,  50,  51, 174, 175, 176, 177, 178, 179, 180, 181
 182, 183, 184, 185, 186, 187, 188, 189, 190
*Elset, elset=_PickedSet13, internal, generate
  1,  36,   1
*Nset, nset=_PickedSet16, internal
*Elset, elset=_PickedSet16, internal, generate
  1,  36,   1
*Nset, nset=_PickedSet17, internal
*Elset, elset=_PickedSet17, internal, generate
 245,  289,    1
*Orientation, name=Ori-1
          1.,           0.,           0.,           0.,           1.,           0.
1, 0.
** Region: (Section-13:Picked), (Material Orientation:Picked)
  1,  36,   1
** Section: Section-13
*Solid Section, elset=_PickedSet13, orientation=Ori-1, material="Fine Grained Beach Zone"
1.,
** Region: (Section-4:Picked)
 37,  39,   1
** Section: Section-4
*Solid Section, elset=_PickedSet9, material="Drain Zone"
1.,
** Region: (Section-1:Picked)
  40,  198,    1
*Solid Section, elset=_PickedSet4, material="Deep Foundation"
1.,
** Region: (Section-5:Picked)
 199,  244,    1
** Section: Section-5
*Solid Section, elset=_PickedSet11, material="Starter Dam"
1.,
*Orientation, name=Ori-2
1, 0.
** Region: (Section-12:Picked), (Material Orientation:Picked)
 245,  289,    1
** Section: Section-12
*Solid Section, elset=_PickedSet12, orientation=Ori-2, material="Coarse Grained Beach Zone"
1.,
*End Instance
*Nset, nset=CGBeach, instance=Part-1-1
*Elset, elset=CGBeach, instance=Part-1-1, generate
  1,  36,   1
*Nset, nset=F, instance=Part-1-1
*Elset, elset=F, instance=Part-1-1, generate
  40,  198,    1
*Nset, nset=Drain, instance=Part-1-1
*Elset, elset=Drain, instance=Part-1-1, generate
 37,  39,   1
*Nset, nset=FGBeach, instance=Part-1-1
*Elset, elset=FGBeach, instance=Part-1-1, generate
 245,  289,    1
*Nset, nset=S, instance=Part-1-1
   1,   2,   3,   4,   5,   6,   7,   8,  11,  13,  14,  15,  16,  17,  18,  19
  20,  21,  22,  23,  24,  25,  26,  27,  28,  29,  30,  31,  32,  33,  34,  35
  36,  37,  38,  39,  40,  41,  42,  43,  44,  45,  46,  47,  48,  49,  50,  51
  52,  53, 110, 111, 112, 113, 114, 115, 116, 117, 118, 119, 120, 121, 122, 123
 124, 125, 126, 127, 128, 129, 130, 131, 132, 133, 134, 135, 140, 141, 142, 143
 144, 145, 146, 147, 148, 149, 150, 151, 152, 153, 154, 155, 156, 157, 158, 159
 160, 161, 162, 163, 164, 165, 166, 167, 168, 169, 170, 171, 172, 173, 174, 175
 176, 177, 178, 179, 180, 181, 182, 183, 184, 185, 186, 187, 188, 189, 190, 191
 296, 297, 298, 299, 300, 301, 302, 303, 304, 305, 306, 307, 308, 309, 310, 311
 312, 313, 314, 315, 316, 317, 318, 319, 320, 321, 322, 323, 324, 325, 326, 327
 328, 329, 330, 331, 332, 333, 334, 335, 336, 337, 338, 339, 340, 341, 342, 343
 344, 345, 346, 347, 348, 349, 350
*Elset, elset=S, instance=Part-1-1
   1,   2,   3,   4,   5,   6,   7,   8,   9,  10,  11,  12,  13,  14,  15,  16
  17,  18,  19,  20,  21,  22,  23,  24,  25,  26,  27,  28,  29,  30,  31,  32
  33,  34,  35,  36,  37,  38,  39, 199, 200, 201, 202, 203, 204, 205, 206, 207
 288, 289
*Nset, nset=SDam, instance=Part-1-1
*Elset, elset=SDam, instance=Part-1-1, generate
 199,  244,    1
*Nset, nset=_PickedSet179, internal, instance=Part-1-1
   9,  10,  56,  57,  58,  59,  60,  61,  62,  63,  64,  65,  66,  67,  68,  69
  70,  71,  72,  73,  74,  75,  76,  77,  78,  79,  80,  81,  82,  83,  84,  85
  86,  87,  88,  89,  90,  91,  92,  93,  94,  95,  96,  97,  98,  99, 100, 101
*Elset, elset=_PickedSet179, internal, instance=Part-1-1, generate
  42,  198,    3
*Nset, nset=_PickedSet180, internal, instance=Part-1-1
  3,  4,  9, 34, 54, 55
*Elset, elset=_PickedSet180, internal, instance=Part-1-1
 35, 36, 40, 41, 42
*Nset, nset=_PickedSet181, internal, instance=Part-1-1
  10,  12, 108, 109
*Elset, elset=_PickedSet181, internal, instance=Part-1-1, generate
 196,  198,    1
*Nset, nset=_PickedSet183, internal, instance=Part-1-1, generate
   1,  350,    1
*Elset, elset=_PickedSet183, internal, instance=Part-1-1, generate
   1,  289,    1
*Nset, nset=_PickedSet184, internal, instance=Part-1-1
   1,   4,   6,   7,  11,  12,  35,  36,  37,  38,  39,  40,  41,  42,  43,  44
  45,  46,  47,  48,  49,  50,  51,  52, 110, 111, 112, 113, 114, 115, 116, 117
 118, 119, 120, 121, 122, 123, 124, 125, 126, 127, 128, 129, 130, 131, 132, 133
*Elset, elset=_PickedSet184, internal, instance=Part-1-1
   1,   3,   5,   7,   9,  11,  13,  15,  17,  19,  21,  23,  25,  27,  29,  31
  33,  35,  37,  38,  94,  97, 100, 103, 106, 109, 112, 115, 118, 121, 124, 127
 130, 133, 136, 139, 142, 145, 148, 151, 154, 157, 160, 163, 166, 169, 172, 175
 184, 187, 190, 193, 196
*Nset, nset=_PickedSet185, internal, instance=Part-1-1
   2,   3,   7,   8,  13,  14,  15,  17,  18,  19,  20,  21,  22,  23,  24,  25
  26,  27,  28,  29,  30,  31,  32,  33,  53, 144, 145, 146, 147, 148, 149, 150
 151, 152, 153, 154, 155, 156, 157, 158, 159, 160, 161, 162, 163, 164, 165, 166
*Elset, elset=_PickedSet185, internal, instance=Part-1-1
   2,   4,   6,   8,  10,  12,  14,  16,  18,  20,  22,  24,  26,  28,  30,  32
  34,  36,  38,  39, 211, 212, 218, 219, 220, 221, 222, 223, 242, 243, 244, 245
 246, 247, 248, 249, 250, 251, 252, 253, 254, 255, 256, 257, 258, 259, 260, 261
 262, 263, 264, 265, 266, 289
*Nset, nset=_PickedSet186, internal, instance=Part-1-1
   7,  12, 136, 137, 138, 139
*Elset, elset=_PickedSet186, internal, instance=Part-1-1, generate
 184,  196,    3
*Nset, nset=_PickedSet220, internal, instance=Part-1-1
*Elset, elset=_PickedSet220, internal, instance=Part-1-1
 288, 289
*Nset, nset=_PickedSet222, internal, instance=Part-1-1, generate
   1,  350,    1
*Elset, elset=_PickedSet222, internal, instance=Part-1-1, generate
   1,  289,    1
*Nset, nset=_PickedSet184_PP_, internal, instance=Part-1-1
*Nset, nset=_PickedSet185_PP_, internal, instance=Part-1-1
*Nset, nset=_PickedSet186_PP_, internal, instance=Part-1-1
*End Assembly
** MATERIALS
*Material, name="Coarse Grained Beach Zone"
*Density
8.,
*Elastic
15000., 0.25
*Permeability, specific=10., type=ORTHOTROPIC
 0.000167, 1.67e-05,       0.,      1.1
  0.00167, 0.000167,       0.,      1.5
*Sorption
-450000.,  0.05
 -70000.,   0.1
   -500., 0.564
    -50., 0.828
     -7.,  0.95
      0.,    1.
*Mohr Coulomb
25.,0.
*Mohr Coulomb Hardening
20.,0.
*Material, name="Deep Foundation"
*Density
8.,
*Elastic
200000., 0.28
 2.4e-05, 0.6
*Material, name="Drain Zone"
*Density
9.,
*Elastic
150000., 0.28
 0.024, 0.9
*Sorption
-70000., 0.027
  -500., 0.246
   -50., 0.535
    -7.,   0.9
     0.,    1.
*Material, name="Embankment Dams"
*Density
6.,
*Elastic
100000., 0.28
 0.00024, 1.1
*Sorption
-70000., 0.027
  -500., 0.246
   -50., 0.535
    -7.,   0.9
     0.,    1.
*Material, name="Fine Grained Beach Zone"
*Density
9.,
*Elastic
10000., 0.26
 0.000167, 1.667e-05,        0.,       1.1
  0.00167,  0.000166,        0.,       1.5
*Sorption
-450000.,  0.05
 -70000.,   0.1
   -500., 0.564
    -50., 0.828
     -7.,  0.95
      0.,    1.
*Mohr Coulomb
10.,0.
25.,0.
*Material, name="Starter Dam"
*Density
6.,
*Elastic
100000., 0.28
 0.00024, 1.1
*Sorption
-70000., 0.027
  -500., 0.264
   -50., 0.535
    -7.,   0.9
     0.,    1.
*Mohr Coulomb
35.,0.
25.,0.
*Material, name="Sublayer Foundation"
*Density
8.,
*Elastic
150000., 0.23
 0.00024, 0.6
*Material, name="Top Layer Foundation"
*Density
8.,
*Elastic
150000., 0.23
 2.4e-06, 0.8
** BOUNDARY CONDITIONS
** Name: BC-7 Type: Displacement/Rotation
*Boundary
_PickedSet179, 1, 1
_PickedSet179, 2, 2
** Name: BC-8 Type: Displacement/Rotation
*Boundary
_PickedSet180, 1, 1
** Name: BC-9 Type: Displacement/Rotation
*Boundary
_PickedSet181, 1, 1
*Initial Conditions,Type=Stress,Geostatic
F, -160, 0, 0, 20, 0.5
*Initial Conditions, type=ratio
F,0.5,0,0.5,15
SDam,1.1,20,1.1,32
Drain,1.0,20,1.0,22
CGBeach,1.6,20,1.6,49
FGBeach,1.7,20,1.7,49
** STEP: Step-1
*Step, name=Step-1, nlgeom=YES
Geostatic In-situe Case
*Geostatic
** Name: BC-4 Type: Pore pressure
*Boundary
_PickedSet184_PP_, 8, 8
*Adaptive Mesh Controls, name=Ada-1, initial feature angle=90., transition feature angle=90.
*MODEL CHANGE, REMOVE
S
** LOADS
** Name: Load-1   Type: Gravity
*Dload
_PickedSet183, GRAV, 10., 0., -1.
** OUTPUT REQUESTS
*Restart, write, frequency=0
** FIELD OUTPUT: F-Output-1
*Output, field, variable=PRESELECT
** HISTORY OUTPUT: H-Output-1
*Output, history, variable=PRESELECT
*End Step
** STEP: Step-2
*Step, name=Step-2, nlgeom=YES
*Soils, consolidation, end=PERIOD, utol=100., stabilize=0.0002
20., 1000., 0.01, 1000.,
*MODEL CHANGE, Add
S
*Boundary, op=NEW
** Name: BC-5 Type: Pore pressure
*Boundary, op=NEW
_PickedSet185_PP_, 8, 8
** Name: BC-6 Type: Pore pressure
*Boundary, op=NEW
_PickedSet186_PP_, 8, 8
*Boundary, op=NEW
_PickedSet179, 1, 1
_PickedSet179, 2, 2
*Boundary, op=NEW
_PickedSet180, 1, 1
*Boundary, op=NEW
_PickedSet181, 1, 1
*Adaptive Mesh, elset=_PickedSet222, op=NEW
** OUTPUT REQUESTS
*Print, contact=YES, plasticity=YES, solve=YES
*End Step
Take a look in the .dat and .msg files - that should tell you what the exact error is.
Martin
Is that the entire .inp file ??
It seems incomplete: did you define any steps, loads ?
I think the forum software truncates any post after so many lines....
Try posting just the step information.
Thank you Martin and Xerf and sorry about missing info. This is every and only thing i get from ERROR under Job Monitor  :
"Analysis Input File Processor exited with an error". where and what . I do not know..!!!!
here is the  input file missing info:
* MATERIALS
*Density
8.,
*Elastic
15000., 0.25
*Sorption
-450000.,  0.05
 -70000.,   0.1
   -500., 0.564
    -50., 0.828
     -7.,  0.95
      0.,    1.
*Mohr Coulomb
25.,0.
20.,0.
*Density
8.,
*Elastic
200000., 0.28
 2.4e-05, 0.6
*Density
9.,
*Elastic
150000., 0.28
 0.024, 0.9
*Sorption
-70000., 0.027
  -500., 0.246
   -50., 0.535
    -7.,   0.9
     0.,    1.
*Density
6.,
*Elastic
100000., 0.28
 0.00024, 1.1
*Sorption
-70000., 0.027
  -500., 0.246
   -50., 0.535
    -7.,   0.9
     0.,    1.
*Density
9.,
*Elastic
10000., 0.26
*Sorption
-450000.,  0.05
 -70000.,   0.1
   -500., 0.564
    -50., 0.828
     -7.,  0.95
      0.,    1.
*Mohr Coulomb
10.,0.
25.,0.
*Density
6.,
*Elastic
100000., 0.28
 0.00024, 1.1
*Sorption
-70000., 0.027
  -500., 0.264
   -50., 0.535
    -7.,   0.9
     0.,    1.
*Mohr Coulomb
35.,0.
25.,0.
*Density
8.,
*Elastic
150000., 0.23
 0.00024, 0.6
*Density
8.,
*Elastic
150000., 0.23
 2.4e-06, 0.8
*Boundary
_PickedSet179, 1, 1
_PickedSet179, 2, 2
*Boundary
_PickedSet180, 1, 1
*Boundary
_PickedSet181, 1, 1
F,0.5,0,0.5,15
SDam,1.1,20,1.1,32
Drain,1.0,20,1.0,22
** STEP: Step-1
*Geostatic
*Boundary
S
** LOADS
*Dload
** OUTPUT REQUESTS
*End Step
** STEP: Step-2
*MODEL CHANGE, Add
S
*Boundary, op=NEW
*Boundary, op=NEW
*Boundary, op=NEW
*Boundary, op=NEW
_PickedSet179, 1, 1
_PickedSet179, 2, 2
*Boundary, op=NEW
_PickedSet180, 1, 1
*Boundary, op=NEW
_PickedSet181, 1, 1
** OUTPUT REQUESTS
*End Step
Which version do you use?
I don't think that the adaptive remeshing in ABAQUS can handle real large element distortion since it doesn't change the mesh topology. In fact, the remeshing method used in ABAQUS is mesh smoothing.
OK, looks to me as if abaqus/pre is failing, so there is a problem with your input file - the line "Analysis Input File Processor exited with an error" is a sure sign of that.
Can you have a look in the job directory and find the .dat file?  Open this file in a text editor and look for the word 'error' then post the error message for us to see.
Martin
Thanks abaaa and other repliers
Dear bassmanjax
Your suggestion is simple yet very effective . You deserve a star.
I discussed this with several users (some of them were experts) no one could help me arrest what and where the ERROR is. Here is the Error
 ***ERROR:  A MODEL CHANGE IS BEING MADE FOR ELEMENT 1 INSTANCE PART-1-1. MODEL
           CHANGE IS NOT  SUPPORTED WITHIN AN ADAPTIVE DOMAIN
 ***NOTE: DUE TO AN INPUT ERROR THE ANALYSIS PRE-PROCESSOR HAS BEEN UNABLE TO
          INTERPRET SOME DATA.  SUBSEQUENT ERRORS MAY BE CAUSED BY THIS OMISSION
The message above implies that I cannot use both ADAPTIVE MESHING and MODEL CHANGE  in the same Step. Well Upon activating my elements under large Defo the model doesn’t run (This was (as I believe) due to large elements distortion)  . That is why I went for adaptive meshing. Kindly and gratefully  do you have any hinting suggestion to deal with is shocking issue.?
Hi
I'm thinking loads and material definitions here, but the only load in the GEOSTATIC step is a gravity load of 10 (I assume that's 10 m/s^2).  I assume therefore that you are using SI consistent units of Nwetons, meters and seconds?
Check your material properties - have you used consistent units to define the elasticity - in this case N/m^2.  If you have mistakenly defined a material that is too soft, the elements will distort excessively and you will not get a converged solution.
Martin
Dear Martin
Thank you for help. The units are uniform. It is just my material that starts to consolidate at high initial void ratio.
Best regards
