Bracing for moment frame

Bracing for moment frame

Bracing for moment frame

(OP)
Dear all,

I am working on a multi-story frame constructed with hollow structural steel.  The client's preference for this is due to hygenice reasons and all my connections are welded moment connections.  I have some horizontal tubes for my structure.  I am wondering whether additional bracing in terms of X- or diagonal bracing on the horizontal platforms would be beneficial.  I do not have any vertical bracing at all due to the constraints of equipment and access.  Any advice?

Thanks.

RE: Bracing for moment frame

Is this in a high seismic zone?  I'm not sure if there are many (if any) approved moment connections between tubes for high seismic.

RE: Bracing for moment frame

(OP)
Here are the 2% PE in 50 year

The 0.2 sec Spectral Response Acceleration is 32.05

The 1.0 sec Spectral Response Acceleration is
12.06

RE: Bracing for moment frame

I'm working on the same problem, client like tubes.  Im my case I talked them into bracing.
For your case, Horizontal bracing only helps if you have a vertical stability system (vert bracing, moment frames, shear walls) in place to transfer lateral load to ground.  

From what you wrote, sounds like you will need to use moment (rigid) frames. This will likely drive up your column sizes to twice what they are now, due to K (effective length factor) and seismic loads are higher for moment frames due to lower R (response) number.

Sometimes the big columns and expensive moment connections will have your client make adjustments and use the "KING OF VERTICAL STABILITY".......X-BRACING>

Ball park loads (guess) will be around 15-20% of mass form moment frame.  Please verify that with code.

hope that helps.


RE: Bracing for moment frame

Diagonals in both vertical planes are the simple solution to lateral load with any shape steel system.  Moment connections and induced bending in the columns/beams is high cost in terms of engineering, materials and rigidity.
Diagonals in the horizontal plane are usually redundant to floors/roofs/slabs.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources