Design Basis for Industrial Air Change Rate

Design Basis for Industrial Air Change Rate

Design Basis for Industrial Air Change Rate

(OP)
Excluding ventilation required for heat load removal and/or contaminant levels various HVAC catalogs (ie Loren Cook, Greenheck,etc) list recommended air change rates for various commercial and industrial facilities.

Of particular interest is the industrial facilities.

What is the design basis to derive the recommended air change rates??

My outdated copy of the "Industrial Ventilation - A Manual of Recommended Practice" does not list suggested air change rates.
The "Steel Mill Ventilation" book (published 1965)appears to be the predecessor to the "Industrial Ventilation" book and does not list recommended air change rates.

  

RE: Design Basis for Industrial Air Change Rate

(OP)
satchmo
Thanks for looking
As I had stated previously, the chart that you referenced is commonly available.  I would like to know how that number was derived.  
I have a client whom insists on air change rate significantly lowered than that published on the recommended frequency charts.
Does anyone know if this topic is covered by the IBC??

RE: Design Basis for Industrial Air Change Rate

You may want to do a search on Sick Building Syndrome and see if there any standard change rates.

RE: Design Basis for Industrial Air Change Rate

I have an old McGraw-Hill Engineering Manual that lists various ventilation rates, which appear to be from ASHRAE of the period.  Among other interesting things, it lists different rates for "normal" schools, and schools for "children of lower socio-economic status".  There is some commentary to indicate that removal of body odors is the basis.  I wouldn't doubt that the industrial rates you note assume that physical exertion is required in these settings, and bump the rates accordingly.  Deodorant wasn't common until the 60's.  Ah, the good old days!

RE: Design Basis for Industrial Air Change Rate

(OP)
Ross
Interesting tidbit of info
ASHRAE probably wishes that you had thrown that ole book away

RE: Design Basis for Industrial Air Change Rate

I/ve used 1.5 CFM/SF in the past, soem local code amendments have half the requirements (MN is one of them at .75 CFM/SF).
I'd go around it this way:

The IMC 2006 allows for an engineered ventilation system, which means that you can provide the high rate for the code reviewer and still satisfy your client by installing combination CO/NO2 sensors or other IAQ sensors for other gases to override the Ventilation system to swicth to the high rate, set the rate as low as possible (even below your client's requirements) any time the IAQ sensor detects limits below OSHA acceptable Threshold Limit values.

RE: Design Basis for Industrial Air Change Rate

In addition to maintaining indoor air quality, depending on the used of the facility the ventilation design could be driven by the heat gains and maintaining acceptable internal conditions.

I went to a baggage handling facility where internal temperatures were fine with about 4ACH ventilation on a 32oC day and and the prime concern there was creating air movement by installing numerous fans around the place.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources