What are good standards to use for loading (PSF) and deflection (inches/span) for maintenance only catwalks.

RE: CATWALK STANDARDS

The Michigan Building Code gives a Live Load for cat walks.  I imagine the IBC would give it also.  As for the deflection I'd think that l/240 would work for the Total Load and l/360 for the Live Load.

RE: CATWALK STANDARDS

IBC gives a catwalk LL of 60 psf.  But this is for catwalks of stages and other assembly type areas.  Its' not clear if it applies to industrial catwalks as well.

RE: CATWALK STANDARDS

ASCE 7-02 gives 40 psf and 300 lb concentrated load as minimum values for "Catwalks for Maintenance Access".

If this is for an industrial project, suggest that you consider at least 60 psf since it may be necessary to take heavy "equipment parts" on the catwalk during maintenance operations.

www.SlideRuleEra.net idea

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources