Single Phase loads on 3-Phase High Resistance Grounded Systems

Single Phase loads on 3-Phase High Resistance Grounded Systems

Single Phase loads on 3-Phase High Resistance Grounded Systems

(OP)
The transformer is 13.8kV - 480V, 2500kVA delta-wye HRG. Through a switchgear the transformer feeds balanced three phase loads i.e. motors and 3-phase step down transformers.

It is proposed to install a 100kVA, 480V - 120/240V single phase transformer on this system to feed an existing building.  Since the HRG system has no neutral, will this affect the secondary voltage on the 2500kVA transformer? Why or why not?

RE: Single Phase loads on 3-Phase High Resistance Grounded Systems

Since the transformer will be connected line-to-line, there should be no problem.  There will be a phase unbalance because two phases will have more load, with some unbalanced voltage drop, but 100 kVA on a 2500 kVA transformer should present no problem.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources