Transformer Connection, Y-Y
|
Transformer Connection, Y-YTransformer Connection, Y-Y(OP)
Is it possible to connect a Y-Y transformer so that the secondary has a 60 degree phase shift. If yes, how is this accomplished.
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: Transformer Connection, Y-Y
Now report back to the group on the Hoepner connection.
RE: Transformer Connection, Y-Y
In practice you can get two possible combinatios: Yy2 or Yy10. Both require the inversion of one side (preferably low voltage side, as hight voltage side could face some dielectric problems). For detaled connetions, let's assume that A, B, C and a, b, c, are HV and LV windings in positive sequence for original transformer Yy0, and A*, B*, C* and a*, b*, c* the new transformer windings. Then:
For Yy2 connection group:
A*=A; B*=B; C*=C; a*=-c; b*=-a; c*=-b
And for Yy10 connection group:
A*=A; B*=B; C*=C; a*=-b; b*=-c; c*=-a
Julian