Async vd Sync Motor Evaulation`
Async vd Sync Motor Evaulation`
(OP)
Just need to ask if I'm missing anything here in this analysis:
Motor Async Sync
Load 1169 1169 KW
Motor Eff 0.96 0.96 %
Gear Box Eff 0.985 0.985 %
Power Factor 0.88 1
hours/day 24 24 Hours
days/year 350 350 Day
$/KWH $0.09 $0.09
Cost Per Year
to Operate $934,607 $934,607
KVAR of Mtr 631 0
KVAR Charge $1.50 $1.50 Demand Charge
Yearly KVAR
Demand Charge $11,357 $0 Cost per year per motor
Motor Cost $55,000 $320,000
Am I correct in seeing that this is a no brainer to go with the async motor? I'm also assuming that the MV motor starters are the same price (when the sync starter is probably 1.3x the cost). In addition, if I'm looking at 5 of these units, and keeping an ROI of 15%, I'd have about $500,000 for capacitors
Motor Async Sync
Load 1169 1169 KW
Motor Eff 0.96 0.96 %
Gear Box Eff 0.985 0.985 %
Power Factor 0.88 1
hours/day 24 24 Hours
days/year 350 350 Day
$/KWH $0.09 $0.09
Cost Per Year
to Operate $934,607 $934,607
KVAR of Mtr 631 0
KVAR Charge $1.50 $1.50 Demand Charge
Yearly KVAR
Demand Charge $11,357 $0 Cost per year per motor
Motor Cost $55,000 $320,000
Am I correct in seeing that this is a no brainer to go with the async motor? I'm also assuming that the MV motor starters are the same price (when the sync starter is probably 1.3x the cost). In addition, if I'm looking at 5 of these units, and keeping an ROI of 15%, I'd have about $500,000 for capacitors





RE: Async vd Sync Motor Evaulation`
RE: Async vd Sync Motor Evaulation`
RE: Async vd Sync Motor Evaulation`
I'm assuming this is a 4 or 6 pole machine based on the power factor quoted. Synchronous motors don't offer any real advantages until at least 10,000KW at this speed (for us anyway). Capacitors are cheaper, easier to control, and more reliable than field excitation systems for synchronous motors at this power level. What is your starting requirement?
Also, you need to consider your system constraints such as available fault (starting) MVA, utility requirements for power quality, site maintenance issues, etc.
RE: Async vd Sync Motor Evaulation`
1250KW
4P/1500 RPM (Using in Portugal)
Rated Speed 1486
Design N
F Insulation
Temp Rise = 80 Deg C
SF 1
IP55/TEFC
Noise 88dB
100% Load PF = 0.87
100% Load Eff = 96.7
Thermistors and space heaters
Nothing elaborate, 24/7 operation.
RE: Async vd Sync Motor Evaulation`
RE: Async vd Sync Motor Evaulation`
A problem I have had with Weg motors is that they tend to produce less torque per amp than other designs. In other words your starting torque may be significantly lower for the amount of power you can give it, which becomes important if you plan to use reduced voltage starting of any kind. It can also mean that if you are running the motor at less that full load, your losses may be a slightly higher percentage of the energy input. You can tell by comparing the efficiency at 75% and 50% load, something any decent motor manufacturer should be able to provide you with.
JRaef.com
"Engineers like to solve problems. If there are no problems handily available, they will create their own problems." Scott Adams
For the best use of Eng-Tips, please click here -> FAQ731-376
RE: Async vd Sync Motor Evaulation`
50% 75% 100%
PF 95.5 96 96.1
Eff 0.81 0.84 0.87
Does anyone have an idea (or even if it possible which I am sure it is) if they even make a 12 pole motor? I can't imagine the cost. BTW, you are correct on leadtime.....52 weeks.
I'd share the quote if anyone is interested. Again, thank you all for your input and advice.
RE: Async vd Sync Motor Evaulation`
respectfully
RE: Async vd Sync Motor Evaulation`
RE: Async vd Sync Motor Evaulation`
If anyone can find it, it deserves to be a FAQ link IMO
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: Async vd Sync Motor Evaulation`
http://w
RE: Async vd Sync Motor Evaulation`
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: Async vd Sync Motor Evaulation`
RE: Async vd Sync Motor Evaulation`
I'm guessing you've got your row labels mixed up in your last post. Otherwise, the Eff seems quite low, and in conflict with your first post.
I didn't notice the motor voltage stated anywhere. What voltage is the motor going to run at?
For every % more efficient one motor is versus the other, you will save on the order of $10G a year, but even considering that, I suspect you would need to see a difference of 5% of so for a business case to suggest selecting the more efficient motor (at the costs you've quoted). That much difference is unlikely.
RE: Async vd Sync Motor Evaulation`
Back in the day they used sync motors as something akin to a virtual gear train to maintain syncronization among stages of a production line, but modern controls have obsoleted that justification.
In addition to the first cost, sync motors have higher rebuild costs and suffer from the disadvantage of relative obscurity -- few service companies have experience with them.
A machine with a rotating exciter will minimize the starter cost penalty -- 30% is excessive. Not surprising, but excessive.
Finally, sync motors are hard to start. If your application requires full load torque while starting an induction motor may well be your best choice.
We are not seeing new applications of sync motors in this size range. Not enough benefit to justify the hassle.
But if you need caps, don't discount the cost of protection and control equipment for the caps. They require a severely derated breaker and instrumentation / relaying that roughly equal the exciter. None of that is significant for a 1MW motor, though.
Basler sells their generator exciters configured for motors, with protection, control, and power supply for rotating exciter machines all in one package. Don't let anyone sell you an old-school exciter package.
Regarding the motor power derating when "making vars" for plant power factor correction: when the sync motors are a significant fraction of the total load, the leading power factor required is small. 95% leading PF is making a lot of vars. Some sync motors are rated for non-unity power factors to begin with. You can run with the stator electrically overloaded by a few percent safely as long as you are monitoring the RTDs.
Finally, take a good hard look at using a sync motor with no gearbox. Lower maintenance, less foundation cost and space, less high-frequency noise. Less capital cost. Less coast-down time. No gear losses = higher efficiency.
None of these considerations will make up for the loss-leader pricing you're getting for the induction motors.
RE: Async vd Sync Motor Evaulation`
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: Async vd Sync Motor Evaulation`
RE: Async vd Sync Motor Evaulation`