Tranaformer Differential
i was just wondering if anyone can help me, by explaining the old Transf. Diff pricipal, using inter-posing CT's. i have not worked on such a system until now. i understand the protection with the new electronic relays but not when you introduce electro-mechanical relays, with iner-posing CT's.
RE: Tranaformer Differential
The main function of an interposing CT is to balance the currents supplied to the relay where there would otherwise be an imbalance due to the ratios of the main CTs.
Interposing CTs also provide a convenient method of establishing a delta connection for the elimination of zero sequence currents where this is necessary.
Ralph Christie
Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376
s to cancel back out the 30° phase shift from prim to sec.
You can connect the 'delta-side' CTs as a'star', and the 'star-side' CTs as a 'delta' to match the phase angles for the electromechanical relay to compare.
As already noted, you can correct for high side / low side turns-ratio current magnitudes with the same CTs.
Also see GE's Art & Science of Protective Relaying, Chapter 11 at http://ww