Autotransformers
Autotransformers
Autotransformers
In the case of bulk power transfer, why is the autotransformer between the two lines grounded WYE: grounded WYE?  ie 500KV:230KV or 230Kv:69KV
RE: Autotransformers
Wye not?  It provides a defined phase to ground voltage and nice clean connections; try to draw out the connection diagram for a delta-delta autotransformer.
Usually to avoid a phase shift. Delta connected autotransformers cause a phase shift.
respectfully
The earthy end of the winding can be insulated to a lower voltage than the line end in a star connected design is used. A delta connection requires the full winding to be insulated for line voltage. At very high voltages the insulation takes up a signficant amount of the core window so the saving can be significant.
  Sometimes I only open my mouth to swap feet...
Try drawing a Delta-Wye autotransformer.
Good one! BJC!
Gunnar Englund
www.gke.org
I had considered saying something about wye-delta autotransformers but the concept was so outlandish I didn't bother.  You could do an open delta autotransformer using two single-phase autotransformers but there just isn't a way to close it.