Chilled Water System

Chilled Water System

Chilled Water System

(OP)
What is the benchmark for the quality of chilled and condenser water? I believe it is measured in ppm of minerals but what type of minerals should we be removing to maintain the good quality?

RE: Chilled Water System

See masterspec 15189 "HVAC water Treatment". Also read the green pages of masterspec, they can help you understand the rational behind things.

RE: Chilled Water System

I would rather say ions. Primarily, Calcium, Magnesium, Carbonates and Silicates have scale forming tendency (but not limited to). Hardness should be generally below 50 ppm and TDS below 300 ppm (500 ppm is the maximum limit)

Either you can keep control on these parameters are use corrosion and/or scale inhibitors to increase the safe levels.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources