Plastic bin storage with high roofs
We constructed a 70000 square foot metal fabrication plant a few years back for a customer. It is fully sprinkled, with a design density of 0.35 gpm/sf.   The eave height is about 55 feet.  The building houses large metal stamping presses.  The customer originally stored both finished and work-in-process parts in noncombustible wire cages.
Their customer is now using collapsable HDPE crates (or stack bins) for parts transport and storage.  They typically stack the bins 4 to 5 high, which yields storage heights of about 20 feet. We have been asked to evaluate necessary changes to the fire protection system.  We are having trouble finding a solution using NFPA 13 due to the excessive eave height.  The building has overhead bridge cranes and 70 foot spans between columns. Anyone have any ideas?
RE: Plastic bin storage with high roofs
A review FM Data Sheet 8-9 and NFPA 13 does not permit this storage because of the excessive clearance height.
As I see it they have the following options, they may not like it, but sometimes we just need to say what u did is not in the books!
1. Have the client store the bins on a dedicated area and lower the ceiling via a suspended ceiling and then upgrade this area with ESFR. Separate this area from adjacent area with a draft curtain.
2. Store the product on a rack and put in-racks at each level of storage.
3. Go back to a wire cages.
4. Store the plastic outside in a trailer.
You may want to post this question on the American Fire Sprinkler Association e-mail forum to.
sprinklerforum@firesprinkler.org