I am working on a natural gas distribution project, and I am looking for some detail or procedure for hot tapping at the existing natural gas piping. The existing piping is 3" and 4" steel underground piping, and the new branch is 2" HDPE. Could anyone advise where I can find the detail or hot tapping procedure?





RE: hot tap natural gas piping
http://ww
http:
jt
RE: hot tap natural gas piping
For Hot Tapping you can follow “Safe Hot Tapping Practices in the Petroleum & Petrochemical Industries API RECOMMENDED PRACTICE 2201” as a reference document
For some inputs on the subject you can go to:
htt
Regards
Luis
RE: hot tap natural gas piping
RE: hot tap natural gas piping
You would need to know what the operating pressure is and the flange rating on the valve in order to get a detail or procedure for hot tapping.
RE: hot tap natural gas piping
-frabricate branch(weldolet and weld neck flange)according to the company's piping standards
-check the thickness of the header where the welolet is to be welded
-make sure there the product is flowing while the branch is being welded
-pressure test brach after it's welded to header
-consider using a full port valve
RE: hot tap natural gas piping
If you *don't* use a full-port valve, how do you expect to get the cutting head through.
Did I miss something from nosabe's message?