Duct work off of an air handling unit is 8' wide (x 4' high) and runs the entire length of one side of a mechanical room at 16" off the floor. What section addresses this? Does the section indicate a 'height off the floor' minimum?
Thanks
Thanks





RE: NFPA 13 Mech room duct obstruction
RE: NFPA 13 Mech room duct obstruction
RE: NFPA 13 Mech room duct obstruction
RE: NFPA 13 Mech room duct obstruction
RE: NFPA 13 Mech room duct obstruction
You have to get the head piped there and be able to get the head put on and take it off. also the four inch minimum 8.8.3.3 2002 edition not sure if it applies.
RE: NFPA 13 Mech room duct obstruction
It's never been the standards intent to require all areas of the floor be wetted either.
This place can't be used for storage so what is there to burn?