NFPA 13 Mech room duct obstruction

NFPA 13 Mech room duct obstruction

NFPA 13 Mech room duct obstruction

(OP)
Duct work off of an air handling unit is 8' wide (x 4' high) and runs the entire length of one side of a mechanical room at 16" off the floor. What section addresses this? Does the section indicate a 'height off the floor' minimum?
Thanks

RE: NFPA 13 Mech room duct obstruction

See NFPA 13, 02 8.5.5.3, and 8.5.5.3.1, no exception for height, provide sprinkler protection under the duct.

RE: NFPA 13 Mech room duct obstruction

Is it 16 inches or 16 feet?? If 16 inches and NO storage below, what will burn?? If 16 feet then see my comments above.

RE: NFPA 13 Mech room duct obstruction

Plus if it is 16 inches, you have to fit the pipe in there and you can have the head up to one foot down, so you might be protecting four inches underneath

RE: NFPA 13 Mech room duct obstruction

(OP)
Thank you for your posts. It is 16 inches. In this case there is minor storage, but at issue is; in a sprinklered room where duct work is an obstruction under 8.5.5.3, is there a height off the floor where the rule does not apply? IE 6"? Is storage under the duct of consequence, for as noted, at 16' sprinklers would be required, storage or not.

RE: NFPA 13 Mech room duct obstruction

would not require it if it is not going to do any good, but have required heads under low duct work.

You have to get the head piped there and be able to get the head  put on and take it off. also the four inch minimum 8.8.3.3 2002 edition not sure if it applies.

RE: NFPA 13 Mech room duct obstruction

NFPA #13 doesn't address every issue and I find it hard to believe the standards intent was to require sprinklers in that space.

It's never been the standards intent to require all areas of the floor be wetted either.

This place can't be used for storage so what is there to burn?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources