Total Power from Unbalanced Heating Amp Measurements
Total Power from Unbalanced Heating Amp Measurements
(OP)
Do I need to do phasor calcs on a system ?
Voltage = 204 206 209
Amps = 32 42 53
What is the power in kW?
P= Pa + Pb + Pc ????
Voltage = 204 206 209
Amps = 32 42 53
What is the power in kW?
P= Pa + Pb + Pc ????






RE: Total Power from Unbalanced Heating Amp Measurements
Also, if you're going to calculate on a per phase basis, you'll want to use to the line-to-neutral voltage, so assuming this is a 208/120V system, divide those voltages by 1.732.
RE: Total Power from Unbalanced Heating Amp Measurements
RE: Total Power from Unbalanced Heating Amp Measurements