Here's one for you guys. Rack sprinklers

Here's one for you guys. Rack sprinklers

Here's one for you guys. Rack sprinklers

(OP)
Back to back double row racks having solid shelves with heads 10' on center staggered between tiers of storage.

Flue space is 6" and every third set of racks straddles the building columns which are 6" steel rounds spaced 40' on centers.

What obstruction clearances apply when the sprinklers get close to the columns?

RE: Here's one for you guys. Rack sprinklers

If I understand what you are asking, I would just apply the "three times" rule and stay 18" away from the columns.

RE: Here's one for you guys. Rack sprinklers

None, see NFPA 13, 02 section 8.13.5 In-racks sprinklers not required to follow obstruction criteria of section 8.5.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources