I am in the process of pouring a containment area in Mississippi.  The slab (60'x70') is to be poured this week, with temperatures hovering around freezing at night and daytime highs around 45 degrees.  My contractor would like to add 2% calcium chloride to the mixture.  This slab cannot have construction joints, only contraction joints every 12 feet or so, and a fear that shrinkage cracking will be an issue with the calcium chloride.  The slab is reinforced with uncoated rebar (#5).  Will the calcium chloride create a corrosion problem in the steel, and if so, what should I substitute instead of the calcium chloride to allow cold weather placement.  Thanks all.

C

RE: Calcium Chloride

Your supplier should use an NCA (Non-chloride Containing Admixture) instead of simple Calcium chloride due to the corrosion potential with your uncoated #5 bar embedded in the slab.  Technically, by following ACI recommendations for embedment depth and assuming that the deck will not be susceptible to the addition of chlorides in service, it would most likely be fine even with CaCl2... but, you never can be too cautious I guess. Bascially everything prior to 1975 or so and placed in the winter was placed with 2 to 3% CaCl2 in it and most of those are still standing...

RE: Calcium Chloride

No chlorides in reinforced concrete.

RE: Calcium Chloride

I always heard don't use chlorides in reinforced concrete but was told that ACI 318 has acceptable amounts based on table 4.4.1.

RE: Calcium Chloride

The maximum percentage in the table for dry, protected from moisture,(not a slab on grade), is one.  Again, not necessary or advisable for placing concrete in above freezing temperatures.

RE: Calcium Chloride

If the slab is covered with insulated curing blankets, it should be okay. Lower temperatures require heat. ACI 304 I believe covers cold weather concrete. If temperatues have been below freezing the rebar should be warmed prior to pouring.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources