Diesel Genset for Class 1, Div. 2
2

Diesel Genset for Class 1, Div. 2

Diesel Genset for Class 1, Div. 2

(OP)
I am looking for a new diesel generator, 160kW, UL rated for operation in a hazardous area, Class 1 Division 2 as defined by the NEC.

CAT was approached, but since the profit margins may be rather narrow on this type of unit, the response has been somewhat dismal.

Anyone have any contacts for OEM's or third party mod shops that can produce this type of unit (UL certified)?

RE: Diesel Genset for Class 1, Div. 2

I don't think you're going to find such a beast; move it to a non-classified location.

RE: Diesel Genset for Class 1, Div. 2

Storage batteries, starting motor, starting solenoid battery charger alternator and most other engine electrics are not commonly available in explosion-proof versions.
Neither are the generator ancilliaries such as the AVR, and the circuit card which provides automatic start and engine monitoring and shut-down.
Alternators themselves are not generally constructed in explosion proof versions.
As davidbeach suggested, move the unit to a non-hazardous area.
Under the Canadian code, any electrical equipment used in a hazardous area must be certified, regardless of voltage. This includes such equipment as flashlights, multi-meters, sound powered telephones, tachometers, pagers and other equipment.
Don't forget the anti-condensation heater and the coolant heater.
Then there is the issue of hot exhausts and turbos.
Your only hope may be to enclose the generator in a pressurised housing, and apply for special permission.
However, if you have space for the collection of fresh, non-hazardous air and the associated blower and filters, you may be able to just mount the genset there in the first place.
respectfully

RE: Diesel Genset for Class 1, Div. 2

Class I division II means that the flammable gases are not present in the area under normal operation and allows non-incendive equipment.  Basically all equipment in div II areas must not produce enough energy to cause ignition of the flammable substance under normal operating conditions of the device.

RE: Diesel Genset for Class 1, Div. 2

I suggest you contact Mark Evans at Clarke Diesel in Cincinnati. 513 771 2200, 800 519 9591 (Eastern Time Zone)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources