Reversal Valve Problem,
We have a Farval greasing system to our equipment. The reversing valve is FR10 if any one knows that, and the coil resistance around 3 Ohms ,
We faced a problem that we cant put a fuse in the output of the transformer less than 10 Amps
Even though the transformer is 250VA , the problem rises when the pressure switch on all the time It burns the transformer and we will lose the coil of the valve even more all the starter fuses will blown
the Transformer voltage is 110 and if the Pressure switch has a problem and no one see that the Transformer will burnt out , any ideas what shall I do ??
F
F
RE: Reversal Valve Problem,
Why can't you put the proper size fuse in the transformer secondary? If it is because the fuse blows on load transient currents, put in a slow blow, time delay fuse. If it is because the fuse holder is too large, put in the proper fuse holder.
but it will not work less than 10 Amps , cause the current during the switching ?!!!
if the PS was okay , every thing will be fine even the fuses for the transformer output should be 2.5A , but the problem is big if the PS shorted and the current goes through the valve
What do you mean by time delay fuse?? I never heard about that and how much time u can put in this type??
Thanks for your help
F
any advice will be appreciated ,
PS: if you want to see the Drawing I can send.
Thanks Again
Fernando
You can not calculate valve current from V/R. The valve coil inductance must be considered. I doubt that it has 3 ohms impedance at the power frequency.
so how much the current will be in this case ???
how much time these fuses will pass on ??
what shall I do in this case ??
F
F
I need to leave soon. I hope some others respond to this post.
AC coils have what is called an "inrush" when you first turn them on. Because of this, fuse manufacturers have what are called "Time Delay" (aka Slow Blow) fuses that allow an initial inrush without blowing the fuse link. While technically you can get into the specific engineering data of the fuse to see the time curves etc., in reality the fuse manufacturers have thoroughly investigated most AC coil applications and know what the delay needs to be. So if you just get an off-the-shelf TD fuse, rated for the coil current of your solenoid, then you will probably be fine. Post the type of fuse you're using know and we can get an idea of the fuse-holder you currently have, which then tells us the TD type fuse you will need.
JRaef.com
"Engineers like to solve problems. If there are no problems handily available, they will create their own problems." Scott Adams
For the best use of Eng-Tips, please click here -> FAQ731-376
Re the cost of Time Delay fuses, less than a transformer.
However, that is like getting a bigger bandaid. If the valves are causing the transformers to burn up, there is a basic design flaw. If you don't find and fix the design flaw you will just blow fuses instead of transformers. It will get expensive.
respectfully
Keith Cress
In your 2nd post you wrote:
"if the PS was okay , every thing will be fine even the fuses for the transformer output should be 2.5A , but the problem is big if the PS shorted and the current goes through the valve"
If this is happening repeatedly, there must be a problem that is causing it. It could be that excessive current due to slow puul-in is welding the contacts. Whatever the cause, it needs to be corrected.
Did you ever contacted the manufacturer of the Greasing system? They are the best people to help you here. With all due respect electrical does not appear to be your field of expertize. Hire someone who knows the greasing system and electrical systems. Start with the manufacturer.
The complete valve model number is FR-10-5(or 9)-volts-Hz. You should check to make sure that you have the correct valve for your voltage and frequency. If you have 50 Hz on a 60 Hz valve, the solenoids would draw too much current.
You should also check the total load on your transformer. The valves alone represent 80% of the loading. A control transformer that is designed to supply starters etc. is designed to supply something like 10 times the VA rating for a very short time to accomodate inrush current without the voltage dropping too much.
Well I agree with you about the inrush current and there is two valves , The name plate says that it's 60 HZ and 120 V , so I think we are fine , but the problem is the the switching time is around 4 sec , so we have high inrush current , do u think that using time delay fuse 2.5 AMPS will help us ?? or do we have to think in another solution ???
F
Keith Cress
In the size of contactors normally supplied from this size transformer, a very slow contactor may have a transit time of 100 ms, or 1/10 second. Most would be considerably faster.
At 4 seconds, I suggest that you call a greasing system expert to examine your valves for mechanical or consumables problems.
Is this system being used with grease much hevier than it was designed for. Has some grease gone hard in the valves? Is the system being used at 40 deg. below, with no heating, or faulty lubrication heating?
Blown fuses may be a symptom rather than a cause. If you treat the symtoms rather than the root problem, the problem will often break out somewhere else. When it does, it is often much harder to solve. Actually, I often find that the correct solution is the simplest.
respectfully