For the convector and radiant panel, if the mean media temperature is the same, is the output of  water and 50% glycol same?

RE: Question about glycol heating media

No:

The specific heat of glycol mixture is less
The conductivity of glycol mixture is less
The viscocity of glycol mixture is more changing the film coefficient....

RE: Question about glycol heating media

Generally when adding glycol you increase the flow rate by using a different pump.  The increased flow rate can compensate for other factors.  However the piping system may need to be bigger to accomodate the increased flow rate.
If you stay with the same pipes you may double your friction head loss.

If you really need 50% glycol figure 1.4 as a ballpark flow rate multiplier.  Unless you are in Siberia you probably don't really need a full 50%.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources