For the convector and radiant panel, if the mean media temperature is the same, is the output of water and 50% glycol same?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Question about glycol heating media
|
RE: Question about glycol heating media
The specific heat of glycol mixture is less
The conductivity of glycol mixture is less
The viscocity of glycol mixture is more changing the film coefficient....
RE: Question about glycol heating media
http://www.raypak.com/commframe.htm
RE: Question about glycol heating media
If you stay with the same pipes you may double your friction head loss.
If you really need 50% glycol figure 1.4 as a ballpark flow rate multiplier. Unless you are in Siberia you probably don't really need a full 50%.