WHY TWO DIFERENT RATING FOR FIRE PUMP?

WHY TWO DIFERENT RATING FOR FIRE PUMP?

WHY TWO DIFERENT RATING FOR FIRE PUMP?

(OP)
I have just read someone’s design drawing for a 30 Horse Power Fire Pump. I am not sure why his design  calls for 250 amp enclosed circuit breaker on the Normal side of the Fire Pump controller ATS on the Normal side and a 50 amp enclosed circuit breaker to the Emergency side of the Fire Pump controller ATS.

I am not sure why this two different rating for Normal side and Emergency side. Can someone explain this concept?

RE: WHY TWO DIFERENT RATING FOR FIRE PUMP?

Check out the Fire Pump article in the NEC and notice the difference in requirements for the utility source and the alternate source.  One has to handle locked rotor current indefinitely and the other doesn't.

RE: WHY TWO DIFERENT RATING FOR FIRE PUMP?

The breaker must handle the LRA of the motor
indefinitely. The conductor is rated at 125%
of the FLA.

RE: WHY TWO DIFERENT RATING FOR FIRE PUMP?

As davidbeach said, the reason behind the two different ratings has to do with what they expect out of the two power systems when feeding the pump that is fighting the fire. When connected to the utility source, they don't want line faults that may occur as other equipment catches on fire to cause the breaker to trip the fire pump off-line just when you need it the most. It's all within the concept of "run to destruction" behind most fire pump rules. The breaker in the backup genset source can be smaller (essentially cheaper) because they recognize that the backup source is limited anyway and not as prone to system wide damage as the fire progresses.

JRaef.com
"Engineers like to solve problems.  If there are no problems handily available, they will create their own problems."   Scott Adams  
For the best use of Eng-Tips, please click here -> FAQ731-376

RE: WHY TWO DIFERENT RATING FOR FIRE PUMP?

(OP)
There is no where in the code [NEC] that we can size it differently/lower for the Normal side though I agree all the reasoning for doing so.

RE: WHY TWO DIFERENT RATING FOR FIRE PUMP?

(OP)
I meant size lower for the EMERGENCY side but have LRC rating for the Normal side

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources