HORIZONTAL CHILLED WATER COPPER SPAN
HORIZONTAL CHILLED WATER COPPER SPAN
(OP)
Dear sirs:
Do you know any standard or basic practice in order to specify spans for insulated cw copper pipe support?.
I am using Type L, diameters 1/2 to 2.1/2 inches.
Thanks,
schola
Do you know any standard or basic practice in order to specify spans for insulated cw copper pipe support?.
I am using Type L, diameters 1/2 to 2.1/2 inches.
Thanks,
schola





RE: HORIZONTAL CHILLED WATER COPPER SPAN
RE: HORIZONTAL CHILLED WATER COPPER SPAN
Hanger spacing shall be as follows:
Horizontal:
Copper Piping Maximum Spacing
3/8" and under 4'-0"
1/2" through 3/4" 6'-0"
1" through 1-1/2" 8'-0"
2" and larger 10'-0"
Vertical: Copper piping shall be supported at 10 feet intervals maximum.
Round rods supporting the pipe hangers shall be of the following dimensions:
2" pipe and under 3/8" rod
2-1/2" to 3" pipe 1/2" rod