Reactive Power Absorption by Series Reactors

Reactive Power Absorption by Series Reactors

Reactive Power Absorption by Series Reactors

(OP)
Is there an equation which would explain the reactive power absorption of a series reactor with impedance X.  Assume that the series reactor between point 1 and point 2.  Thanks for any help.

RE: Reactive Power Absorption by Series Reactors

Use Ohm's law to determine the current. (Voltage divided by impedance. E/Z)
Use Ohm's law to determine the reactive component of the current. (Current times reactance. IX rather than the more familiar IR)
respectfully

RE: Reactive Power Absorption by Series Reactors

Actually, the voltage used for that Ohms Law solution would have to be the voltage drop across the series reactor. If you could determine that, then you would have to multiply it by the reactive current, not the total current(x sqrt3 for 3-phase), to get the reactive power.

You should be able to determine the current flow through the reactor based on the downstream load (or the FLA of the reactor), and then use I^2(R + jX)=(P + Q), or just I^2X=Q, Q being Reactive Power.

RE: Reactive Power Absorption by Series Reactors

(OP)
I have heard quite a bit about series reactors on high voltage line were intentionally use to mitigate potential high fault current, but inadvertently, block (absorbs) excessive VARs in the system.  How does this actually work? and by what magnitude (proportionally) to the impedance value of the Series reactor?  Is it true that the voltage drop corresponding to the series reactor the same per unit factor as the impedance of the series reactor (i.e. a SR with .02 per unit will suggest a voltage drop of .02 p.u as the effect of this series reactor.)  Thanks for the help.

RE: Reactive Power Absorption by Series Reactors

It's just an inductance.  Put it in the circuit and do the calcs.  There is nothing magic about it.  Just another circuit element.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources