Chilled Water Precision Air Handling Unit
Dear sirs:
I've been estimating chilled water cooling coil "delta P", finding  very diffferent values among common manufacturers ( DataAire (45 ft H2O), Liebert (10 ft), , APC(20 ft). for the similar equipment
Do you have a rough or practical standard value?
schola
RE: Chilled Water Precision Air Handling Unit
I would consider 10 mormal, 15 is getting high.
Take the "V" out of HVAC and you are left with a HAC(k) job.
5 psi or 10 ft is our usual allowance in absence of submittal data
The above replies are noraml ranges of DP.  But the DP can be different depending on the Cv and the flow rate.  You can use the :  Q= Cv sqrt(DP) equation to calculate any DP and flow rate Q, if you know the Cv of the equipment.
Remember, the higher the DP, the higher you have to pay in energy for pumping the fluid through the equipment.
regards,