minimum live load for tresury areas (in banks)
5

minimum live load for tresury areas (in banks)

minimum live load for tresury areas (in banks)

(OP)
dear members
hi and happy new year. would you please guide me about the minimum live loads which should be considered in tresury    and deposit ( safebox) areas  in central office of banks?
have a nice day

RE: minimum live load for tresury areas (in banks)

You may want to check with them and determine an actual weight.  Could be 100 psf or 400 psf depending on how high the piles of money are...

Dik

RE: minimum live load for tresury areas (in banks)

Heavy filing systems generally run around 200 to 250 psf.  That value is also similar to commercial kitchens with heavy equipment.  I would suggest at least 200 psf - but would definitely look into the actual weight of the containment drawers/boxes and estimate some contents to see how the load spreads out in a uniform value.

RE: minimum live load for tresury areas (in banks)

recently worked on an existing federal reseve bank and the floor design loads ranged from 250 psf to 600 psf depending if they were storing coin or not.

Definetly check with your client

regards,

RE: minimum live load for tresury areas (in banks)

I worked on a design of a payroll building - constructed of timber only. The safe was pretty heavy. The floor joists were 2x12 @ 8 in o.c. The joists were supported every 2 ft. I bet if you back-calculate you'll be in the ballpark of 400 psf or something like that.

RE: minimum live load for tresury areas (in banks)

I would worry about the point load caused by the heavy equipment moving the safe to the right spot.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources