Abandon an existing manhole

Abandon an existing manhole

(OP)
I am working on a sewer line replacement project and I was wanting to know the proper way to abandon an existing manhole.  I was thinking of plugging the sewer line with concrete, remove the top manhole ring and fill the manhole with no. 57 gravel except for the last 2 feet which would be top soil.  Please let me know if there is a better way to do this.

RE: Abandon an existing manhole

If you filled it with gravel and topsoil, you'd be creating a large, buried bucket.

How deep is the manhole and will the sewer continue as a solid pipe through the manhole or near by? Or is the sewer line being abandoned too?

RE: Abandon an existing manhole

(OP)
There will be about 40 manholes that are going to be abandoned that range from 4 feet to 15 feet deep.  The sewer line is being abandoned too.  

RE: Abandon an existing manhole

I did something very similar with a lift station.

I asked the contractor to drill some holes in the bottom of the lift station for drainage, remove the top 3 feet of the structure, and then backfilled the lift station with aggregate.

If you have a deep manhole, you would require a large hole if you wanted to completely remove the structure. You would have to replace more pavement and worry about adjacent structures. That is expensive and unnecessary.

RE: Abandon an existing manhole

I have used CALTRANS spec:

15?2.05A   Frames, Covers, Grates, and Manholes

?    When existing manholes or inlets are to be abandoned, pipes entering the manhole or inlet shall be securely closed by a tight fitting plug or wall of minor concrete not less than 150-mm {0.5-foot} thick, or by a tight brick wall not less than 200-mm {0.67-foot} thick with cement mortar joints.  Minor concrete shall conform to the provisions in Section 90-10, "Minor Concrete."  The bases of manholes or inlets shall be broken in a manner to prevent entrapment of water.  The manhole or inlet shall be demolished to an elevation one meter {3.5 feet} below finished grade and backfilled in conformance with the provisions in Section 19-3.06, "Structure Backfill."

Good luck

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources