FM200 with HVAC Smoke Damper

FM200 with HVAC Smoke Damper

FM200 with HVAC Smoke Damper

(OP)
Could anyone advise why the smoke dampers are required at HVAC supply and return duct for the electrical room protected by FM200 system? Which code should I refer to for this requirement? I am wondering if FM200 control panel can shut down the air-handling unit instead of smoke damper in case smoke is detected in the room?

Thank you for advise.

RE: FM200 with HVAC Smoke Damper

The reason smoke dampers are required is to ensure the design concentration is maintained. Fire dampers are designed only to limit the spread of fire. They do limit the spread of smoke, but smoke dampers are designed to accomplish this and are more efficient.

Most dampers currently in the market that are listed as meeting UL standard 555 are combination fire and smoke dampers.

See the following requirement from Section 5.3.4 of NFPA Standard 2001, which governs the design and construction of clean agent fire suppression systems:

To prevent loss of agent through openings to adjacent hazards or work areas, openings shall be permanently sealed or equipped with automatic closures. Where reasonable confinement of agent is not practicable, protection shall be expanded to include the adjacent connected hazards or work areas or additional agent shall be introduced into the protected enclosure using an extended discharge configuration.

RE: FM200 with HVAC Smoke Damper

(OP)
Thanks, Stookeyfpe. It looks the A/C unit with 100% return air does not need to be shut down when the fire or smoke is detected per NFPA2001.

RE: FM200 with HVAC Smoke Damper

Your goal is to create a gas tight compartment, unless your design tolerates the leakage of the agent. Read the entire standard, not the parts that make you think your design will work for the given application

I am not chastizinging.  Rather, make sure that the design compensates for leakage.

RE: FM200 with HVAC Smoke Damper

(OP)
Thanks again, Stookeyfpe.

Have great holidays and happy new year!

RE: FM200 with HVAC Smoke Damper

The last few FM200 room we did use a VESA system for sampling and control of the smoke dampers. Upon the low level smoke, all the CRAC units were turned off and dampers “failed” to the closed position. Upon increase in smoke FM200 release.
http://www.vision-fs.com/opencms/opencms/system/modules/com.vfsportal/default_bodies/apac/int_en/products_fire_landing.html
UL555 – class 1 is the ultra low leak dampers. I like to use Greenheck
http://www.greenheck.com/products/dampers/smoke.php

RE: FM200 with HVAC Smoke Damper

I wouldn't trust a Vesda detector on its own to shut down HVAC and release FM200.
The first false alarm (and they happen often in some datacenters), you will be crying.
At least use two and cross zone them.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources