Mimimum sq ft for not having suppression

Mimimum sq ft for not having suppression

Mimimum sq ft for not having suppression

(OP)
Is there a minimum sq ft reg for not having to install suppression?  like less than 200 sg ft ?   I read the bathroom and closet stuff.  But what about just another small room ?  

RE: Mimimum sq ft for not having suppression

depends on what code you are using and what you are trying to apply it  to.

is this an apartment, motel/ hotel, house, ????????

RE: Mimimum sq ft for not having suppression

(OP)
An industrial area, a 300 sg ft abbrasive bead blasting room.  The walk in room is inside a type 1 suppression protected space.   Essentially, a room inside a room.  

RE: Mimimum sq ft for not having suppression

So is it a room or an enclosure? If it is an enclosure you may be able to get around the requirement because it is a piece of equipment.

And I doubt if any of us know what a Type 1 Suppression Protected Space is.

You need to give us additional information

-- Automatic sprinklers throughout (yes/no)
-- Occupancy
-- Construction type and building area
-- What is the bead blast material?

RE: Mimimum sq ft for not having suppression

(OP)
It is a walk in room (equipment), this room is inside a room that is protected with a suppression system. Automatic sprinkler throughout, industrial occupancy, construction type is steel and  concrete, the bead blast media is plastic.

I hope this helps some.

RE: Mimimum sq ft for not having suppression

sounds like it needs to be protected and would not meet an exception. basicaly nfpa 13 says sprinkle through out unless you meet an exception.
My take is if you can walk in it sprinkle it. and since the building is sprinkled it should be very simple to sprinkle this room

Is this a room designed to suppress the sound of the blasting???

does it look like this or did some one build a room out of say sheet rock
http://www.titanabrasive.com/blrmspec1.html

RE: Mimimum sq ft for not having suppression

(OP)
It is being installed by a manufacture, it looks very similiar to the on on that web site.  
Do you knoe the pargaph in NFPA 13 that mentions sprinkler, unless exception ?  

RE: Mimimum sq ft for not having suppression

basicaly the entire book but specificaly 8.1.1 (1-6) NFPA 13 2002

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources