Ground Grid Study

Ground Grid Study

Ground Grid Study

(OP)
Hydro provides customer with maximum and minimum short circuit currents as well as max Z and Z0 values.
If the ground grid study needs to be done. I was told to use Max( L-L-G, L-G) for ground fault.
Why do we need max and min values? Where Min is used in calculation?

RE: Ground Grid Study

Typically, minimum Short Circuit values are used to verify pickup of protective devices at the lowest amount of fault current available, and this is usually for GF devices.

Minimum values are also used when performing Load Flow or Motor Starting studies.

RE: Ground Grid Study

Ground grid studies typically require a determination of how much fault current will use the ground grid under study vs. other parallel paths which may exist to the source (neutrals or static/shield conductors).  Typically the maximum L-G or L-L-G fault current is much larger than that portion which actually contributes to grid potential rise because the remainder of the current uses other paths available.  If the fault occurs at the grid under study (max If) then the current flows in the grid not through it to earth............thus minimal grid potential rise to remote earth.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources