(OP)
I've been given a project where the surrounding area is rated IIG2.  The new equipment I am installing is IIG2, but the existing equipment is not rated. Even worse, the non-rated equipment must be moved to make room for the new equipment, but will stay in the same IIG2 location.

1. Am I obligated to have the existing equipment rated?
2. Can I non-rate the area around the existing equipment and if so how?

RE: Rating hazardous locations (NEC 70-500).

What type of equipment is involved?  In many cases standard equipment can be used in Class II, Division 2 areas.
Don

RE: Rating hazardous locations (NEC 70-500).

The existing equipment either shall be replaced with rated, or moved out of the classified area.
regards

RE: Rating hazardous locations (NEC 70-500).

I generally agree with resqcapt19, and less so with l3city.

In Class II Div 2 areas, general-purpose equipment is usually OK so long as it is dust-tight and not spark-producing.  Lighting must be rated.  But non-sparking equipment, such as motors, transformers, wire splices, etc., are only required to be dust-tight.  There are many Div 2 light fixtures that look identical to GP fixtures except for the label affixed to them.  You need to take a pretty close look at some Div 2 installations to notice the difference between them and general purpose installastions.

Note also that the boundary between general purpose and Div 2 areas might not be the same as the room perimter.  Some areas of the room might be defined as general purpose, and GP installations would certainly be acceptable in those areas.

RE: Rating hazardous locations (NEC 70-500).

With respect but I based my opinion on your following comment: "The new equipment I am installing is IIG2, but the existing equipment is not rated"
From my part, I'll keep my word as long the existing equipment is not rated.

"peebee" says: "general-purpose equipment is usually OK so long as it is dust-tight and not spark-producing. Lighting must be rated". Again, with respect, but I don't see why "peebee" doesn't agree since you said exist. equip. is not rated. (I'm confused)

Also, as "peebee" says: "But non-sparking equipment, such as motors, transformers, wire splices, etc., are only required to be dust-tight" I agree with this, but if existing motors, they shall also be one of the following totally-enclosed types: Non-ventilated, Pipe-ventilated, water-air cooled, Fan cooled.
There are of course also different requirements for fixtures in Class II, Div II, no matter if existing or new.
Regards

RE: Rating hazardous locations (NEC 70-500).

By "rated" I meant "rated for use in IIG2 areas".  Lighting and arc-producing equipment must carry such ratings; other equipment must only meet the requirements outlined above and is not required to be IIG2 rated.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources