Precast Hollowcore Concrete Slabs
I was looking at the best way to anchor a Hollowcore Precast concrete slab to a bond beam. my outer wall is composed of 4" face brick with 1/2" air space, then 8" CMU. I have a 10" Hollowcore Precast Concrete Slab for the roof slab which will be bearing on top of a 8" Bond Beam which runs the top course around the building. Is there a better way to anchor it other than just running a dowel from the bond beam into the slab, and for construction-detailing purposes, how is that done to anchor it using dowels? Do they just specify and drill where the dowels will be then grout solid or? Any knowledge is appreciated.
RE: Precast Hollowcore Concrete Slabs
Nonbearing end: You can knock out the top of the slab at the first core and insert a hooked or U-shaped rebar that connects the slab to the wall.
The area above the top of the block and the top of the slab and the outside of the block will get cast in place.
h
DaveAtkins
http
on one project, the contractor cut reinforcing at AHU penetration (contractor did NOT need to enlarge the design opening) - Flexicore designed steel frame to transfer load to adjacent panels.