Is there a way to insulate a sanitary sewer pipe for an aerial crossing? The pipe is DIP, 8".
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Sewer line aerial crossing
|
RE: Sewer line aerial crossing
RE: Sewer line aerial crossing
RE: Sewer line aerial crossing
http://ww
www.SlideRuleEra.net
RE: Sewer line aerial crossing
There is however some basic information concerning the structural design and support etc. of uninsulated ductile iron pipe on supports and bridge crossings available from DIPRA at dipra.org (and also some in AWWA Manual M41 (Manual of Water Supply Practices Ductile Iron Pipe and Fittings).
RE: Sewer line aerial crossing
RE: Sewer line aerial crossing
htt
The normal insulation for an application like you describe is a fiberglass insulation 2" thick. The fiberglass insulation is protected with jacketing. The jacketing is either plastic, aluminum, or stainless steel. Stainless straps are used to hold the jacketing on.
What you have to consider is the design temperature, and possible exposure to road salt (damage to jacketing).
http:/
http://www.dipra.org/pdf/bridgeCrossings.pdf