Bolt Installation Procedure
I was inquiring about an installation procedure for Type 325 bolts ranging from 1/2" - 1 1/2" for Structual. This should include Torque values, bolt tensions,etc.
Lapizo
Lapizo
RE: Bolt Installation Procedure
"Allowable stress design"
"Specification for Structural Joints Using ASTM A325 or A490 Bolts"
You should find your answers there
jeff spoor
email at flaminganvil@yahoo.com
ironworker
Bolt Geometry." The lenght of of bolts shall be such that the end of the bolt will be flush with or outside the face of the nut when properly installed".
He should not require a bolt any longer than required to meet the above requirement.
Depending on the type of connection i.e. threads included in a shear plane, threads excluded, slip-critical, if the bolt is to long you could exceed the thread lenght and run into the thread run-out( the shank of the bolt without threads). If this occurs, validation of required tensioning is questionable.
Washers are not required for all connection using A325 or A490 bolts.
When washers are required they should be kept to a minimum (2)one under nut and one under bolt head if required.
How can I get in RCSC to download "Allowable stress design"?
thanks
Thank you for the information, it helped me as well !
Stephen
LnTxn@aol.com
Rod