MV(20kV) Vacuum circuit breaker and surge arrester

MV(20kV) Vacuum circuit breaker and surge arrester

MV(20kV) Vacuum circuit breaker and surge arrester

(OP)
Hi, i've got a tough dilemma regarding 20kV-Vacuum circuit breakers.
Do you possibly know about any requirements for installing surge arresters and where I have to mount them (i mean the surge arresters) on the bus-bar system or on every incoming bushing?

RE: MV(20kV) Vacuum circuit breaker and surge arrester

I've seen them on the breaker, and on the load side in the cells.

RE: MV(20kV) Vacuum circuit breaker and surge arrester

From top of my head, surge arrestors could help protect the breakers and/or loads from switching transients too, not only transients coming from utilities.

Utility companies do not want customer's surge arrestors on the line side of the incoming breakers,as they come in the way of performing a hi-pot tests on their feeders. (Surge arrestors could operate on hi-pot tests, Not good).

So I would place surge arrestors on the load side of the incoming bus or not provide any if the feeder breakers have them. For feeder breakers, I have seen mostly on the load side.

RE: MV(20kV) Vacuum circuit breaker and surge arrester

I would locate surge arrestors where the greatest exposure occurs (usually on the incoming or outgoing power line side of the breaker) or where the clamping will do the most good (nearest the device to be protected).

Within enclosed switchgear there may be limited space for surge arrestors, and you should seek the factory recommended location so as not to encroach on required phase spacing.

RE: MV(20kV) Vacuum circuit breaker and surge arrester

Surge arresters with MV (22 &33kV) vaccum breakers is to avoid the trasient surges from vaccum switching  to come to down line equipment.So it has to be on after CB, normally with a surge absorber capacitor.In India, when 33kV VCBs were originally used to replace oil CB,furnace transformers down line failed,some times on first switching, due to switching surges unique to VCB.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources