GSU Transformer Clearances

GSU Transformer Clearances

GSU Transformer Clearances

(OP)
Hi,

We are replacing GSU transformers. The new ones are taller than existing. I am wondering if anybody is aware of issues related to GSU tansformers clearances to the HV line.
The new transformers contain also more gallons of oil. I am wondering if anybody is aware of issues related to the oil containment curb.

Thanks,

Yigo.

RE: GSU Transformer Clearances

If you're in the US, you need to follow the NESC requirements for clearances.  The new 2007 version is just out.  The clearance depends on the voltage.  

Oil containment is generally sized to contain the entire volume of oil for the largest transformer in the yard.  But this is not a Code issue in the US.  You generally don't even have to have oil containment - just have a plan (and money) to deal with the consequences of a spill.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources