Deflection limits...not just L/360
Deflection limits...not just L/360
(OP)
I know typically deflection limits for LL is L/360 and for D+L it is L/240 in general for stell framed construction(offices, apartments, etc...). I have always used a rule of thumb of limiting deflection to 1/2" total, which usually causes a ratio in the neighborhood of L/500 or so and gives me much heavier sections.
Am I being too conservative limiting to 1/2"?
Am I being too conservative limiting to 1/2"?






RE: Deflection limits...not just L/360
DaveAtkins
RE: Deflection limits...not just L/360
RE: Deflection limits...not just L/360
RE: Deflection limits...not just L/360
RE: Deflection limits...not just L/360
L/600 for masonry or tile floors
L/360 for wood floors is OK....
If you have walls or partitions on the floor in question - these help a LOT in killing vibrations and bounce.
30' x 30' great rooms without any walls are murder. A 250 lb man walking across that will cause havoc unless you have at least L/480. All the dishes in the hutch will rattle!!!
RE: Deflection limits...not just L/360
After the discussion here, I am considering just using L/360 as the limit for D+L deflection, that way I know I have L/360 for LL alone, and it will cut down on my calcs (I am having to do this all by hand & spreadsheets I've made). Also, I will adjust my numerical deflection to 1" allowable.
Sound Ok?
RE: Deflection limits...not just L/360
Plus, you will also add 3/4" plywood and nail it to the joists. You are creating a composite section so your joists are actually stiffer. I would just worry about the defelction ratio instead of the actual deflection unless you are sizing a header above a huge window or something.
RE: Deflection limits...not just L/360
Total deflection is important, but for floor elements, live load only deflection limits also shall be checked per code limits.
RE: Deflection limits...not just L/360
Your building sounds large to be designing by hand. If you plan on doing many of these buildings, you might want to look at purchasing RAM Structural System. Very easy to use, very fast, and not that expensive. No need to buy all of the modules though. Just a thought. Make some money.
RE: Deflection limits...not just L/360
Believe me, you dont need to tell me we need some software. Our office is not equipped to be doing designs like this and i think we sort of got talked into taking this project on as "favor". Being that i am the only one with structural experience in the office, it has fallen to me. I have made it pretty clear to those in charge that if we are going to be getting more of these, we MUST buy something. It's a lot of number crunching and a lot of guestimating to carry all the loads downward to support network below....and a lot of my time.
While we're on the subject, any opinions on RAM vs RISA vs STAAD? I've used STAAD in the past at a previous job, but it'd be rather pricey for this office to absorb.
RE: Deflection limits...not just L/360
You are suggesting eliminating calculation of live load deflection and do L/360 for TL. This doesnt always work. Where I work I have scenario where the live load is very big (80+ psf snow) so Probably the L/480 live load will control. I also size beams to support walls with heavy stone veneer, roof with some roof load. With this scenario my Total load L/240 will probably control. I just think using excel is not very effective especially if you have multiple point load at various locations, distributed load that only go half the way. This is very time consuming to do it by hand and especially to find deflection!!!
RE: Deflection limits...not just L/360
RE: Deflection limits...not just L/360
I have experience with Staad Pro, RAM, Risa 3d. For buidling design, no question, RAM is the one. Designs are very fast and if you set up the exports correctly, your plan work and elevations are created for you, just add notes and pretty it up.
Call them up and ask for a free demo cd. Tech support is great also.
Staad tech support is horrible.
Risa 3d is a good product for finite analysis, tech suupport is great.
RE: Deflection limits...not just L/360
RE: Deflection limits...not just L/360
RAM should be purchased for the design of the entire building. Does not do wood unless you purchase RAM Advanse. RAM does steel, concrete and joists. Or you can add the properties of other materials.
RE: Deflection limits...not just L/360
What state are you located?
RE: Deflection limits...not just L/360
RE: Deflection limits...not just L/360